I think you need a Heating Engineer to assess the pipe work and rad sizes before you do anything.
I wouldn't personally 'try' changing the pump because it won't be cheap and it may not be necessary.
Different sizes of pipe deliver different flow rates per hour. It is possible that 15mm is undersized and that would give the symptoms you describe.
 
Has this just happened ,did you inherit the system , did it work correctly before ?
 
Thanks once again for all your replies. To answer each query, the entire system was a brand new install in 2005 with all brand new pipe work being above ground. The pipe work from the boiler is 22 mm but it all becomes 15 mm as it feeds into the radiators. All exposed pipe work is 15 mm and the living room one is fed by 15 mm pipes from other rads. All the rads are original standard type from the install in 2005. The problem has not always existed. Is it time to call out a heating engineer. Thanks again, Jason
 
Thanks once again for all your replies. To answer each query, the entire system was a brand new install in 2005 with all brand new pipe work being above ground. The pipe work from the boiler is 22 mm but it all becomes 15 mm as it feeds into the radiators. All exposed pipe work is 15 mm and the living room one is fed by 15 mm pipes from other rads. All the rads are original standard type from the install in 2005. The problem has not always existed. Is it time to call out a heating engineer. Thanks again, Jason

If it worked ok from day one , it cant be pipe sizing , gut instinct as I have said earlier is probably the pump , we have a way of testing them lol , but I wont tell you how , please report back on any findings.
 
My living room radiator is cold when all the other radiators are firing. I have checked all the internet YouTube advice feeds. The trv is working correctly, the lockshield valve is also working and I have taken the radiator off and flushed it through and have bled it. I believe it is the furthest from my combi boiler. I have turned all my other radiators off and this makes the living room radiator work, but as soon as I turn one other radiator on the living room one goes back to cold. Any further DIY advice would be much appreciated. Thanks Jason

Have you had your system converted? Probably from a back boiler to a combi? Or from a boiler in one part of the house and your new boiler re-sited?
Sometimes plumbers connect into the 15mm branch, instead of connecting back into the 22mm 'source' pipework.
This can result in balancing issues too bad to 'fine tune' by adjudting radiator valves alone.
 
As previously mentioned the whole system was newly fitted in 2005. There have been no further updates or additions since then apart from the current boiler being fitted in 2008. Thanks for your question. I'm still waiting to get hold of an engineer. Thanks Jason
 
Try and remove the trv head and see does it make a difference they can play up sometimes as someone previously said if it worked from day one it's a process of elimination good luck with it
 
Status
Not open for further replies.

Reply to One radiator will not stay hot in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all, Looking for some advice please. Got a building, all one level with 7 radiators. 3 individual ones in separate rooms then 4 radiators...
Replies
2
Views
317
Hi all. I noticed this winter my living room rad only get hot in the top half. Radiator is 1600mm(DP SC) double panel single convector. System...
Replies
1
Views
454
Hi, Sorry if question already answered in previous posts, but I can't find a solution to the below: We recently moved house to a new home that...
Replies
7
Views
529
I have a slightly undersized radiator in my living room. The calculation says 6315 btus and my rad is 6019 btus. It was a replacement radiator...
Replies
1
Views
340
Free running radiator change. I currently have 1 radiator free running with all of the others fitted with TRV's. Problem is that the free running...
Replies
1
Views
321

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock