Search the forum,

Discuss Newly installed combi losing pressure in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
H

hedylaura

We just spent £3k+ upgrading our old open-vented system boiler system to a new combi condenser boiler (Viessmann 30kw) system which worked less than a week before the pressure dropped to 0 resulting in no hot water or heating. The plumber came and topped up the system saying it was "just one of those things" that happens occasionally for no discernable reason. So I duly paid him for his work. Then a few days later it happened again.

Now the plumber is saying ("in his opinion") that we have a leak in the pipework on the ground floor. He reasoned this because one of the radiators on the top (first) floor had completey drained, and had it been a leak on the top floor there would be signs of it on the ceiling. He topped it up again as a temporary measure so we were able to have hot showers on our return from a trip to Oz, but by the time we got back (less that 24hrs later) it had dropped to zero again.

He is suggesting re-piping the entire ground floor, which will ruin our flooring.

I can't see any evidence of a leak, and we had the place checked for damp not so long ago and this did not flag up any problems in the areas where we have pipework.

So my questions are - is he right? And are there any other ways to determine if/where there is a leak without going to the extreme lengths of ripping up flooring? Is it possible that the plumber caused the leak by over-pressurising the system?

And more importantly - am I liable for the additional costs that this will incur? In my view he hasn't finished the job he set out to do - we did not just buy a boiler off him, we bought hot water and heating. Both of which have been supplied for no more that a week in total since the installation 1 month ago.

Thanks for your help!

Hedy
 
Was it just a boiler upgrade using the original radiators and pipework?
 
was
Is it possible that the plumber caused the leak by over-pressurising the system?

It is always a concern when changing from open vented to a sealed system that the old pipework may not be up to the pressure required for a sealed system. This is something I would have pointed out if I was the plumber. The PRV should kick in at 3 bar so it couldn't have gone over 3 bar so I would say he has not caused a leak by over pressurising but the old copper was not up to the job.

There could be another issue so I will ask this. What was the pressure when you topped it up when cold?
 
was

It is always a concern when changing from open vented to a sealed system that the old pipework may not be up to the pressure required for a sealed system. This is something I would have pointed out if I was the plumber. The PRV should kick in at 3 bar so it couldn't have gone over 3 bar so I would say he has not caused a leak by over pressurising but the old copper was not up to the job.

There could be another issue so I will ask this. What was the pressure when you topped it up when cold?

Not sure, I haven't been there the times he has topped it up.
 
Just spoke to him on the phone. I asked if there any way of testing the system before committing to ripping up the floor, and he said no, unless we wanted to isolate the downstairs pipework from the system and wait for a week to see if there was any pressure loss. This doesn't seem like too bad a prospect, we can hole up upstairs for a few days and at least we'll have hot water, but he was clearly trying to talk me out of it.

It also took a while to hammer him down on how much it would cost. He eventually said around £400. I expressed my discontent at having to pay for this when in my view, this should come under part of his quote which says (and I quote) "Re-pipe to accomodate new position or system type" as the old pipes clearly do NOT accommodate the new system type.

To be fair to him though, NONE of the other plumbers we got quotes from ever highlighted a potential problem with switching to a sealed system with old pipework. Wishing we just got a new cylinder now because the old boiler was fine...
 
my contract clearly states i wont be held responsible for leaks caused by increases in pressure on existing system, and it should not be his fault either, its one of these things which happens unfortunately, not all the time, but sometimes. How big a leak ? how long does it take to loose pressure ? adding leak sealer to the system may help
 
Not sure, I haven't been there the times he has topped it up.

The system should be around 1 bar when cold. Read the boiler manufacturers instructions for their recommendation. I state this as if you say it doesn't look like a leak I would eliminate the possibility that theres too much pressure in the system to start with. If its filled to 2 bar for example as the water is heated the pressure increases and the pressure relief valve may open making the system lose pressure. Check this first (pressure when cold 1 bar).

As someone just said leak sealer may be a good option if the pressures are confirmed to be correct.
 
my contract clearly states i wont be held responsible for leaks caused by increases in pressure on existing system, and it should not be his fault either, its one of these things which happens unfortunately, not all the time, but sometimes. How big a leak ? how long does it take to loose pressure ? adding leak sealer to the system may help

Less than 24hrs. He said that he did not recommend using leak sealer with a brand new boiler. Do you know why this is? I was not shown any kind of contract before the work was carried out. If I'd known this and the potential risks I would have thought again. Plumbers hold all the knowledge and therefore have a duty to the customer to let them know all the risks and what they are/are not liable for.
 
I have never had to use leak sealer on a new boiler so will have to look into that one myself, but when changing from an open vented system which has a pressure of 0.1-0.3 bar roughly, to a sealed system which will have a pressure of 2bar(+/-) when hot, then there is a good chance of leaks on the existing pipework, this must be made clear as if it does happen customer will blame the installer. I explain this and have it in my terms and conditions so once customer signs it I am no longer liable.
 
He should have informed and made clear the issue about older fittings/pipework not being upto the task for a new higher pressure system.
If this was definitely not mentioned he should carry some of the cost to make good the system as far as I am concerned.

Only non-evasive option is to try leak sealer. This can have good results depending in size of leak. Other than that, some exploratory work under floors is only other option.
 
I have never had to use leak sealer on a new boiler so will have to look into that one myself, but when changing from an open vented system which has a pressure of 0.1-0.3 bar roughly, to a sealed system which will have a pressure of 2bar(+/-) when hot, then there is a good chance of leaks on the existing pipework, this must be made clear as if it does happen customer will blame the installer. I explain this and have it in my terms and conditions so once customer signs it I am no longer liable.

Thanks for that. I will check the paperwork that I signed and see if he has a similar clause.
 
If you were in the plumbers position would you be willing to say it was your fault?
 
If you were in the plumbers position would you be willing to say it was your fault?

If I had been the plumber I would not be in his position right now because I would have felt morally obliged to point out the potential risks, just as GrahamM, above.
 
You can't expect him to be liable for the entire existing 20 ish year old system surely?
 
the plumber can only be liable for what he has installed, but he should have advised of the risks, i have had a few leaks caused by upgrading boiler to sealed system
 
You can't expect him to be liable for the entire existing 20 ish year old system surely?
The point is the potential issues are clear and should have been highlighted to the customer. If this was not made clear or even mentioned, the installer has been neglectful and should incur some of the expense to put right in my opinion.
 
You can't expect him to be liable for the entire existing 20 ish year old system surely?

The point is that he withheld information from me that could have altered my decision of what kind of system to go for. We had the system replaced because our cylinder was leaking, so we had the choice to simply replace the old cylinder or upgrade the whole system to a more efficient one. The latter option was sold to us on the basis that it would save us money in the long run. Now we're going to have to fork out for more pipework on top of the 3k already spent, and have to replace god knows how much flooring. Don't think this will be the cheaper option in the long run any more...
 
It's not really his fault, even if you kept same system it could have been a problem who is to know it hasn't been leaking for a while and topping itself up all the time from the f&e tank? I would keep filling it up and looking for leaks best you can and just fix the leak if you find it and not the whole downstairs
 
didnt you say the installer already said to you the difference in pressure could cause problems ?
 
I wouldn't personally keep filling the system up as this can lead to rapid sludge build up in the system. There are company's out there that can trace leaks under floors. I would google it and see if it's cheaper than the 400 quoted.
I wasn't having a personal dig at you in my earlier post. But there's only so much that the enineer can be responsible for. As said above the leak could've been there for years and with the old system you never would've known.
 
As an aside he also kindly relieved us of our ~8 year old perfectly serviceable boiler which could have fetched a couple of hundred quid on ebay, a 1 year old mid-position valve and also our old enormous copper cylinder which I understand can fetch a hundred quid or so as scrap these days. So I think it even more fair that he at least contribute to this extra work. Swings and roundabouts, eh?
 
lol couple of hundreded for an old boiler??your havin a laugh arent you ?

8 years old ? what make and model?
 
Ah the joys of scrap. Did he take all the packaging and cardboard and polystyrene away? People never mention that!:!blank:
 
It's not really his fault, even if you kept same system it could have been a problem who is to know it hasn't been leaking for a while and topping itself up all the time from the f&e tank? I would keep filling it up and looking for leaks best you can and just fix the leak if you find it and not the whole downstairs

There may well have been a leak before. But as the pressure in the system has now increased around 100 fold (~0.1 bar for an open-vented system to 1 bar for a sealed system) I expect the discharge through the leak has also increased 100 fold.
 
thats 10x laura, not 100, and if the leak was already there then he can almost certainly not be held responsible. I'm afraid these things happen and its a shame, but he should have been clear about the problems and if you were willing to take the risk.
 
"To be fair to him though, NONE of the other plumbers we got quotes from ever highlighted a potential problem with switching to a sealed system with old pipework. Wishing we just got a new cylinder now because the old boiler was fine..."
 
He should have pointed the risk out to you but you sound like you're out to get him now. Would you prefer that he left all the scrap/rubbish for you to deal with? His quote would have taken into account the scrap value of the cylinder, if you were keeping it then it would have been added onto the price for the job.
 
Ah the joys of scrap. Did he take all the packaging and cardboard and polystyrene away? People never mention that!:!blank:

Not all of it! He left loads of bits of pipe and packaging around the place. He also left the remnants of his lunch - a kebab. Which festered in our house for a while before we realised where the smell of fermenting onions was coming from...
 
Not all of it! He left loads of bits of pipe and packaging around the place. He also left the remnants of his lunch - a kebab. Which festered in our house for a while before we realised where the smell of fermenting onions was coming from...

Messy pup! That is not good.
 
Not all of it! He left loads of bits of pipe and packaging around the place. He also left the remnants of his lunch - a kebab. Which festered in our house for a while before we realised where the smell of fermenting onions was coming from...

Haha that did make me chuckle. Sorry. I think the bottom line is if you were to take this matter further I'm 99% sure he wouldn't be held responsible. You obviously need to sort the problem but if you have no faith in the installer then it may be better to get the work done through a third party. It's unfortunate but as said by others these things happen from time to time.
 
Status
Not open for further replies.

Reply to Newly installed combi losing pressure in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
252
Hi, basic question, any insight much appreciated. Looking to have an outdoor tap in my front porch fed from 15mm pex coming up from suspended floor. Pic 1 is inside porch, pex temporarily clipped to give an idea of pipe placement (ignore shoddy blockwork of booted cowboy builder!), Pic 2 is...
Replies
6
Views
234
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock