Hi. Our builders hit a problem with extending the balanced flue through a new extension. Their solution was to have the outer, intake pipe terminate at an external wall, but add an extra section to the inner pipe to take the exhaust away from the next house. However, the gas boiler was repeatedly shutting down and they have had to remove the extra pipe for now. The boiler is a GlowWork Flexicom.

Can anyone answer these theories as about why the boiler might be shutting down:

1) The inner and outer pipes should end at the same point
2) The extra pipe has two sharp bends, which is causing extra resistance
3) The weather is very cold, resulting in excess condensation on a 2m external run of flue.

Any other ideas gratefully received.

Many thanks in advance.
 
The bends your describing are fine if they indeed are a plume kit , ( I'm not saying the installation is fine), however you say they've been put in to take combustion away from a nieghbouring house so sounds a bit alarming and Defo needs a gas safe registered engineer to check rather than a builder as for all we know it's been dangerously fitted and struggling to work, please contact your local engineer to have a look ,
 
Thanks for your replies, everyone. The bodge arose because the planned vent through the extension roof was not possible. We think we have a better solution now, but will take up your suggestion of getting 3rd party qualified opinion. In the meantime we would like to dispute the installation I have sketched. Further research tells me that the inner and outer pipe ends need to be in close proximity and the sketch shows significant separation.

Flue.png
 

Reply to Must balanced flue inner and outer be the same length? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all, came across this forum this looking for information on my sooting up kitchen type indoor Enviromax. I'm a retired electronics/maintenance...
Replies
5
Views
2K
Hi, our Bunded 1000ltr plastic domestic oil tank leaking from inner to outer skin, was installed, as part of a new-build, in 2016, to supply a...
Replies
9
Views
2K
L
  • Locked
Hi guys Really need some help... We have a Warmflow 70/90 Oil Fired Combi Boiler. We're looking at putting a porch/conservatory on to the...
Replies
11
Views
2K
Dotty
D
  • Locked
hi all, can anyone recommend a storage boiler So far the Gloworm Energy S with the discharge valve at the top is favorite due to height issues and...
Replies
0
Views
67
  • Locked
Hello i'm new to the forum, I've done a little searching on here and still have questions. Some history... I had 11 double rads in my house then i...
Replies
10
Views
3K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock