12
Hi

Can you help me determine if my new Navien lcb700 lsx is working as expected?

I got the Navien oil boiler installed to replaced an old firebird boiler. The new boiler is a condensing oil boiler and I’m not sure if this is working as expected. I’ve a 300 L water cylinder and after one hour of heating the water temperature reaches 40-45C. The cylinder is less than a year old and the thermostat is working well.

When the heat demand is on, the boiler themostat is set to 60C. The burner starts and the boiler lcd panel reaches 60C. The burner will stop and the pump continues to run. When the temperature at the boiler drops to 40C, then the boiler will burn again to 60C. The cycle continues and the 60C to 40C drop takes about 20 minutes.

My question for anyone….is this normal?

Thanks
 
Unvented cylinder?
 
That’s great do you know the size of the boiler kw ?
 
As the coil on the cylinder is 22kw yes you will have some cycling also with the cylinder temp increasing this will also increase cycling/ time before it fires the boiler again
 
As the coil on the cylinder is 22kw yes you will have some cycling also with the cylinder temp increasing this will also increase cycling/ time before it fires the boiler again
Hi
Am I incorrect to expect the boiler to continue to fire until the water in the cylinder has reached the thermostat set temperature?
 
Hi
Am I incorrect to expect the boiler to continue to fire until the water in the cylinder has reached the thermostat set temperature?

Yes or until the boiler is upto temp then it will wait until the temp drops below its threshold then refire and repeat
 
It will be around an hour due to the coil being miss matched
 
Internal or external pump ?
 
Yea something isn’t right any chance of a picture of the airing cupboard?
 
Hi

Yes, my airing cupboard with my cylinder and the heatmister control area.

The 90 won’t heat the water when it is the only active zone.

Thanks
 

Attachments

  • IMG_2200.png
    IMG_2200.png
    2.2 MB · Views: 17
  • IMG_2199.png
    IMG_2199.png
    2.1 MB · Views: 18
There’s a red wheel headed valve above the ufh stuff is that open fully ?

You coil is big enough now due to you having a twin coil system in series
 
Try closing it half way eg 3 turns
 
Any other potential issues that could be responsible?

Could be supply pipes from the boiler not fully clear / restriction as I would say that coil would easy heat the cylinder up within the hour
 

Reply to Is my Navien boiler behaving as expected? in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
198
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
538
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m...
Replies
6
Views
301
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
421
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock