Lycanfox

Thanks in advance for any replies to this.

Basically this morning a hot tap would not turn off and was gushing hot water. I couldn't find an isolation valve for the tap so had to turn off all the water via the main stopcock. The only worry is a plumber I rung said that without the cold water going to our combi boiler, the heat exchange could melt itself and cause a lot of damage so we had to turn our heating off.

Now correct me if i'm wrong but surely as long as the hot water setting is turned off on the boiler, the boiler should have two different heat exchangers so the hot water one would not melt due to not having any water to heat if it was off, and the heating exchanger works on a closed loop so should also be ok?

Thanks again for any replies, the last thing I want is to destroy my boiler in such a cold winter.

Adam
 
Depends on the boiler
 
Hi and welcome to the forums. You should get a plumber out to fix your tap and then you won't have to worry about your boiler.

I normally switch all boilers off at the spur switch when turning off the mains water to a property.
 
As far as I know it is a Ferroli Combi F30 D (I think). With a dual heat exchange for hot water and then for central heating.
 
Just turn it off at the wall to be safe
 
without stepping on anyone's toes you wont have a problem. it is safe and imo your plumber is wrong, do as system3 says andget a decent plumber to fix your tap
 
He will be out tomorrow ASAP to fix the tap, I was just wondering for the moment.

What is a spur switch by the way? As Ideally I would like to keep my central heating on but the water off.

Hi and welcome to the forums. You should get a plumber out to fix your tap and then you won't have to worry about your boiler.

I normally switch all boilers off at the spur switch when turning off the mains water to a property.
 
Tyvm.

Getting one out tomorrow morning to fix it....bloody old houses!

without stepping on anyone's toes you wont have a problem. it is safe and imo your plumber is wrong, do as system3 says andget a decent plumber to fix your tap
 
He will be out tomorrow ASAP to fix the tap, I was just wondering for the moment.

What is a spur switch by the way? As Ideally I would like to keep my central heating on but the water off.
hi, as said leave it on, you wont have a problem
 
you could isolate the cold to the boiler which will isolate all hot taps and then turn your cold mains back on so you have water.
 
Turn it on, take the chance, have your heat excahnger changed for ÂŁ200-300 in 6 months
leave it off, dont take the chance, save ÂŁ200-ÂŁ300.

I know which one I would do.
 
As far as I know it is a Ferroli Combi F30 D (I think). With a dual heat exchange for hot water and then for central heating.

If its the ferroli Im thinking of then the ch and dhw pipework run through the same heat exchanger, such that if you turn off the cold feed to the boiler, the hw side will run dry or part dry, so there is a risk of the remnants in the hex to boil away and even pressurise up as stem if things go wrong. In this situation you should leave the hot in let and oulets open to avoid hex problems, being thats going to be a pain in the bum, just dont use the boiler till the taps repaired, simples and cheapest option. Saves you getting a popping and hissing noise from the boiler
 
If its the ferroli Im thinking of then the ch and dhw pipework run through the same heat exchanger, such that if you turn off the cold feed to the boiler, the hw side will run dry or part dry, so there is a risk of the remnants in the hex to boil away and even pressurise up as stem if things go wrong. In this situation you should leave the hot in let and oulets open to avoid hex problems, being thats going to be a pain in the bum, just dont use the boiler till the taps repaired, simples and cheapest option. Saves you getting a popping and hissing noise from the boiler
that model is the modena he
 
I came across a much older model that wasnt condensing with dual hex fm memory, didnt study it in detail as it was going in the scrap pile, anyway dancin hop it and go back to your hot water bottle and pmt, nicking my one good thought of the evening:46:
 
Last edited by a moderator:
If it boiled the domestic hot water then it would boil the heating water as well, the boiler won't fire on H/W demand and the heating water circulating will be enough to dissipate the heat providing it is working correctly that is (debatable I suppose being a ferroli)
 
Last edited:
If it boiled the domestic hot water then it would boil the heating water as well, the boiler won't fire on H/W demand and the heating water circulating will be enough to dissipate the heat providing it is working correctly that is (debatable I suppose being a ferroli)

not if the runs thro the hex are separate supplies.
 
I came across a much older model that wasnt condensing with dual hex fm memory, didnt study it in detail as it was going in the scrap pile, anyway dancin hop it and go back to your hot water bottle and pmt, nicking my one good thought of the evening:46:
think you are the one thats hoppin lol not me
 
It will be fine just use your heating like normal get some one out to fix your tap and then your be back running like normal.
 
If its the ferroli Im thinking of then the ch and dhw pipework run through the same heat exchanger, such that if you turn off the cold feed to the boiler, the hw side will run dry or part dry, so there is a risk of the remnants in the hex to boil away and even pressurise up as stem if things go wrong. In this situation you should leave the hot in let and oulets open to avoid hex problems, being thats going to be a pain in the bum, just dont use the boiler till the taps repaired, simples and cheapest option. Saves you getting a popping and hissing noise from the boiler

You do realise that water boils at 100c and I have not yet come across a boiler that heats up to 100c in normal operation so I cannot see the problem. If anything it would cause more of a problem when its full of water as the water has to expand so I think your sprouting absolute rubbish.
 
You do realise that water boils at 100c and I have not yet come across a boiler that heats up to 100c in normal operation so I cannot see the problem. If anything it would cause more of a problem when its full of water as the water has to expand so I think your sprouting absolute rubbish.
think lame is saying that any water left in dhw side will expand in the heatex from the ch side as its dualpass and this could cause probs unless a tap is opened, as op says hot tap is stuck open there will be no probs imho
 
I'll try to explain why I gave the advice I did

if the water is running through the hex it wont boil stage 1.
but if the water is not moving and just sitting there theres a good chance its going to get hotter than planned stage 2
which is why low water content boiling are prone to problems when you allow this to happen stage 3

so you never want a situation where the waters able to potentially boil, which is why the likes of chris brown from ferrolli spends most of his time going out to new installs where the installer has failed to prime the water pump and the water in the hex boils melting the flow switch and blowing all the o ring seals on the boiler.

Prehaps thats why I would advice you not to use a boiler with your problem unless you open up the inlet/outlet to prevent risk of boiling.

and dancin got there first again
 
Last edited by a moderator:
Dual heat exchanger in the older models. so if you loose your cold water to the hot water side it will cook nicely. Best advice is do not use without a cold water supply. No service valve up to the offending tap then?
 
Last edited:
think lame is saying that any water left in dhw side will expand in the heatex from the ch side as its dualpass and this could cause probs unless a tap is opened, as op says hot tap is stuck open there will be no probs imho

I still think hes sprouting rubbish as its usually full of water at mains pressure so I cant see the problem the boiler has an overheat which will stop it boiling and the heat exchanger is designed to with stand the pressure of mains water.
 
Overheatstat will kick in on this boiler, at 80degrees "with any luck". But this is a distressing fault condition temperature for the poor old heat exchanger. Why take the risk? Could right off the boiler for the sake of waiting for a tap repair.
 
I still think hes sprouting rubbish as its usually full of water at mains pressure so I cant see the problem the boiler has an overheat which will stop it boiling and the heat exchanger is designed to with stand the pressure of mains water.

but you just hit the nail on the head there, mains is off as the tap is leaking so its not at mains pressure, so water can boil at 100 deg c and lack of water can let it boil, produce steam which can be quite high pressure which can also damage the o rings and cause leaks. Hence why all low water content boiler have overrun to cool the hex to prevent hot spots etc cooking them. So the only one spouting rubbish is milsy
 
How can high pressure steam be produced when the tap is open

bit of water left in the pipework (clutching at straws here :) ), but the main issue is you could fairly easily cause damage when there no need to if you dont use the boiler, why risk it??
 
but you just hit the nail on the head there, mains is off as the tap is leaking so its not at mains pressure, so water can boil at 100 deg c and lack of water can let it boil, produce steam which can be quite high pressure which can also damage the o rings and cause leaks. Hence why all low water content boiler have overrun to cool the hex to prevent hot spots etc cooking them. So the only one spouting rubbish is milsy
the ch side is still full of water and will dissipate the latent heat in the hex
 
How can high pressure steam be produced when the tap is open

No it will just boil the heat exchanger dry. Oh we still have the overheat stat. I wonder what the boilers potentiometer will think of this.
 
Last edited:
would any of the leave it its ok, who have a ferrolli like this at home, pop out and set it up to see what happens in this situ and let us know pse
 
its safe to leave the heating running even with no mains feed it will only fier for heating and the water flow keeps the hex at normal temps and pump will over run to dissipate het when boiler goes of
 
forgot, plumbers dont work on sundays unless callouts ÂŁ200 plus :sleeping:
 
There is no way that the boiler firing up for heating is going to cause any damage to the heat exchanger because the DHW side is empty The pump will run and this will take the heat out of the boiler. Yes there is still going to be water in the DHW side but at zero pressure it will not build up so drastically that it is going to cause damage to the heat ex. As for the OH stat it will also cut the boiler out on the DHW side of things as well as the heating it is a safety feature that will shut the boiler off when heat exchanger gets to a set temperature. It will not do any thing to the potentiometer as every OH stat I have ever come across in the 14 years I have worked in this trade work the same they go from closed to open circuit.

I have left many peoples heating running in the past whilst I have had the water off changing taps etc and surprise surprise I have never killed anybodys heat exchanger. I would suggest Lame plumber that you do not comment on things you are 100% sure of as in this case you are definately sprouting rubbish.
 
we can all have an opinion, but there's no need to be rude, after all forums are for discussion and everyone has had different experience of boilers and problems and because of issues I have had, esp with a ferrolli in the past I offered my opinion such that the bloke posting a query could make a choice. Like I said, I've experienced a ferrolli doing just this when I failed to bleed a pump thro recently, it only wrecked a couple of o rings but when chris from ferrolli turned up, he was decent enough to point out loads of his work involves repairing boilers where the hex is boiled and o rings blown and flow valves melted, and with that damage pcbs etc knackered. This is being done regularly on new installs so there is the potential to do the same with this boiler if your luck runs out so why risk it. So as you tried to say, you shouldnt comment on things you are not 100% sure of, but in this case I'm 98% sure so I think I can offer an opinion without being told I'm sprouting, sorry spouting a lot of rubbish. If you want to comment, please feel free, its an open forum but dont get arsy as its not really needed. After all the guy only wants an opinion to make his choice! be it yours or mine or someone elses
 
There is no way that the boiler firing up for heating is going to cause any damage to the heat exchanger because the DHW side is empty The pump will run and this will take the heat out of the boiler. Yes there is still going to be water in the DHW side but at zero pressure it will not build up so drastically that it is going to cause damage to the heat ex. As for the OH stat it will also cut the boiler out on the DHW side of things as well as the heating it is a safety feature that will shut the boiler off when heat exchanger gets to a set temperature. It will not do any thing to the potentiometer as every OH stat I have ever come across in the 14 years I have worked in this trade work the same they go from closed to open circuit.

I have left many peoples heating running in the past whilst I have had the water off changing taps etc and surprise surprise I have never killed anybodys heat exchanger. I would suggest Lame plumber that you do not comment on things you are 100% sure of as in this case you are definately sprouting rubbish.
sorry but your wrong,end of argument,as said this boiler has a twin pass heat exchanger,there is a risk that remnants of water left in the domestic side can cause issues if the ch is used,now who has the balls to argue differently with me about boiler design??? i am not taking anyones side but this is FACT
 
we can all have an opinion, but there's no need to be rude, after all forums are for discussion and everyone has had different experience of boilers and problems and because of issues I have had, esp with a ferrolli in the past I offered my opinion such that the bloke posting a query could make a choice. Like I said, I've experienced a ferrolli doing just this when I failed to bleed a pump thro recently, it only wrecked a couple of o rings but when chris from ferrolli turned up, he was decent enough to point out loads of his work involves repairing boilers where the hex is boiled and o rings blown and flow valves melted, and with that damage pcbs etc knackered. This is being done regularly on new installs so there is the potential to do the same with this boiler if your luck runs out so why risk it. So as you tried to say, you shouldnt comment on things you are not 100% sure of, but in this case I'm 98% sure so I think I can offer an opinion without being told I'm sprouting, sorry spouting a lot of rubbish. If you want to comment, please feel free, its an open forum but dont get arsy as its not really needed. After all the guy only wants an opinion to make his choice! be it yours or mine or someone elses
nothing to do with the dhw side then ??
 
sorry but your wrong,end of argument,as said this boiler has a twin pass heat exchanger,there is a risk that remnants of water left in the domestic side can cause issues if the ch is used,now who has the balls to argue differently with me about boiler design??? i am not taking anyones side but this is FACT
how and why ?
 
Ok, so whats the difference between this and the heat exchanger on the DHW side being full as you would find in normal operating circumstances? So for example, the heating has been on all night and no one has run the tap. Late at night the tap is run. The water in the DHW side does not get anywhere near boiling point otherwise it would be lethal as it comes out the tap (the volume of water contained within the heat exchanger all night)

The reason is because the heating side is dissapating the heat, which is exactly the reason why the heat exchangers are joined. If there were 2 completely seperate heat exchangers being primarily and directly heated by the burner then this would occur. Remember this is a heat exchanger and its primary purpose id to be able to transfer heat efficiently. Having a twin pass means the 2 act like a big heat sink to one another.

The reason (in my opinion) lame plumber, you had said problem is because you had no flow in either DHW or heating, therefore no way of dissipating that heat, the boiler cannot react quick enough to shut down so the static water boils (or as near as)
 
Last edited:
Status
Not open for further replies.

Reply to Is a combi boiler safe with NO mains cold water? (Urgent) in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi All Bit of an urgent one being that time of year and can't get a plumber out until after xmas even on an emergency callout I have just...
Replies
2
Views
328
M
Hi, I woke up this morning with cold water (mains) from downstairs tap but no hot water from downstairs tap, and no water at all from all the...
Replies
0
Views
245
Mike Young
M
I live in an apartment block where generally hot water is supplied from the communal hot water cylinder and cold water to bathrooms is supplied...
Replies
4
Views
640
Hi, I need some urgent advice. I've Just come home after going out for evening, to discover hallway floor and kitchen floor covered in water. On...
Replies
1
Views
534
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer...
Replies
4
Views
296
Back
Top