Came across one today only 400mm from openable door! MI's state 1200mm! Ar or ncs I at risked it as I was unsure.
 
See I read that as next to any opening In to the dwelling

10. From an opening in a car port (e.g. door or window) into dwelling 1200mm

You saying I should have gone with this?


1. Directly below an opening window, air vent or other ventilation opening 300mm

I went with the first as it was the only one that mentioned door and was not below the terminal
 
See I read that as next to any opening In to the dwelling
10. From an opening in a car port (e.g. door or window) into dwelling 1200mm
You saying I should have gone with this?
1. Directly below an opening window, air vent or other ventilation opening 300mm
I went with the first as it was the only one that mentioned door and was not below the terminal
only 1200mm if under a car port, otherwise its the 300mm
 
assuming we are using the same song sheet here.

Flue Terminal Positions Min. Spacing*
1. Directly below or alongside an opening
window, air vent or other ventilation opening. 300mm (12")
2. Below guttering, drain pipes or soil pipes. 25mm ( 1")*
BS5440-1 2000 75mm (3")
3. Below eaves. 25mm (1")*
BS5440-1 2000 200mm (8")
4. Below balconies or a car port roof. 25mm (1")*
BS5440-1 2000 200mm (8")
5. From vertical drain pipes or soil pipes. 25mm (1")*
BS5440-1 2000 150mm (6")
6. From an internal or external corner or to a 25mm (1")*
boundary along side the terminal. BS5440-1 2000 300mm (12")
7. Above adjacent ground, roof or balcony level. 300mm (12")
8. From a surface or a boundary facing the terminal. 600mm (24")
9. From a terminal facing a terminal. 1,200mm (48")
10. From an opening in a car port
(e.g. door or window) into dwelling. 1,200mm (48")
11. Vertically from a terminal on the same wall. 1,500mm (60")
12. Horizontally from a terminal on the wall. 300mm (12")
Vertical Terminals
13. Above the roof pitch with roof slope of all angles. 300mm (12")
Above flat roof. 300mm (12")
14. From a single wall face. 600mm (24")
From corner walls. 1000mm (40")
Twin Flue Applications
15. Centre distance between air inlet and flue
outlet ducts. 120mm (5")

I'm sure this point has been raised before, the confusion comes with the term "door" mentioned only in the section dealing with a car port. But window is also mentioned there as well as in point -1
so the term to focus on is "opening" = door, window, air vent etc
 
Yeah but what happens when you incorrectly classify an appliance causing undue stress etc and then the customer seeks redress through the courts. scary thought but it's happened and no doubt in this blame and claim society it's always a possibility.
 
Status
Not open for further replies.

Reply to Ideal Mexico balanced flue in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi guys. I'm trying to identify a toilet model before ordering a seat for a customer. I went to what used to be a Roca stockist (they no longer...
Replies
2
Views
172
  • Sticky
Morning to any Australians lurking around! Register its free, then message me, I'll sort your account out for you. We will need a moderator from...
Replies
0
Views
103
Hi, basic question, any insight much appreciated. Looking to have an outdoor tap in my front porch fed from 15mm pex coming up from suspended...
Replies
6
Views
297
IS IT POSSIBLE TO ADJUST THIS MIXER UNIT? WE HAVE TO HAVE IT TURNED ALMOST FULLY ANTI CLOCKWISE TO GET HOT WATEROUT. THE FRONT PLATE WITH MIRA ON...
Replies
6
Views
275
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock