70
Hello,

We are looking to replace our 50yr old heating boiler in a open vented system with a new 100kw boiler, or possibly 2 x50kw. The GB162 requires a sealed system, which would require a plate heat exchanger. It seems that the Evomax 2 can connect to an open vented system without a heat exchanger. Which one would you go for (assuming the Evomax was adequately protected with magnetic and non-magnetic filters)? The current system does not have any filters, but we woudl chemically flash it prior to the instalation.

Thanks
 
Pressurised boiler through plate heat exchanger.
Open vented system for existing system with filters on the inlet side of the return piping back to the heat exchanger.

You will never clean the amount of gunk out of the old system you need to to protect the new boilers.
- It's an open vented system 50 years old -
 
Your new investment wouldn't last a year or two if that (and numerous call outs) if it were directly connected to your old heating circuit (without plate separation) no matter what the claims.
 

Reply to Idal Evomax 2 100kw vs Worcester Bosch GB162 100kw ? in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
139
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
476
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
212
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock