This pump curve is from a combi boiler with an internal automatic bypass valve.
curve.png

Why is the maximum flow obtained with the bypass valve in the middle position? Shouldn't a fully closed bypass valve result in a higher flow through the main circuit?

Also, any idea what 'V1' and 'V2' mean (no clues in the boiler manual)?
 
V1 and v2 boilers ??

Also the bypass won’t operate until the pressure is overcome so probably had a higher pressure spring than the pump force on an open circuit
 
Could V1 and V2 have any special meaning besides versions of this particular model?

I follow your sentence about the bypass operation, assuming it is some type of spring loaded valve. But this does not explain the curves. The blue, red and black curves must have been generated with the valve held into a particular position and in this situation I would expect the red and black to be swapped.
 
All modern pumps are variable speed with different modes/settings, you could have 3 CC settings, 3 PP settings and 3 CP settings, each of these will have a different closed valve (dead headed) head so perhaps something like that.
 
Had a scan through that but really none the wiser, it states that the bypass is automatic and non adjustable which probably means just a spring loaded bypss so the pump speed is controlled automatically to give a certain by pass based on operating conditions like flow/return dT etc. The pump curve only gives one V1 curve (bypass closed), also don' know what 35W means on all curves, 35W would be a typical A rated pump power.
Other info is that the 24kw boiler max outputs are 17.6kw/24kw, heating/DHW and the 28kw boiler max outputs are 23.4kw/28kw, heating/DHW but with probably the same circ pump.
 
All modern pumps are variable speed with different modes/settings, you could have 3 CC settings, 3 PP settings and 3 CP settings, each of these will have a different closed valve (dead headed) head so perhaps something like that.
If the pump is integrated into the boiler, this may not be possible to adjust. Perhaps the boiler manufacturer saw fit to have the pump made so as to only operate in one mode?
 
The blue, red and black curves must have been generated with the valve held into a particular position and in this situation I would expect the red and black to be swapped.
Proportional pressure pump set to increase head with flow might, hypothetically, send more flow around system with the bypass open, though seems unlikely.
 
You can set up a pump in PP mode with a fixed springloaded ABV to pass a certain flow but as system demand increases so too does the pump head in PP mode which forces the ABV to recirculate more, the opposite to what you require, thats why PP mode is not recommended for external ABVs, constant curve (fixed speed) mode was traditionally the proper mode but all modern pumps now control a good portion of their flowrate in a constant pressure fashion even when running in PP mode, the UPS3 is one of the best (or worst) examples of this.
Its likely IMO that the above pump control is done in PWM mode where invinitely adjustable speed is used depending on the flow and boiler temperature conditions, especially the flow/return temperatures dT.

1680599295652.png
 
I would expect the red and black to be swapped.
I agree, the graph key has been muddled up. I think you have a simple pump with two speeds (V1=black, V2=green) and a simple bypass valve that can be closed, part-open (red), or fully open (blue). There'd be no point using V1 with the bypass open as it would essentially give the same performance as the green and red curves but use more electrical power in the process. I suspect that the V1 setting will use more power, say 45W rather than 35W.

These are the sort of errors that get introduced when technical graphs from engineers are 'redrawn for publication' by non-engineers.
 

Reply to Help me understand this pump curve in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
143
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
123
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
250
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
243
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock