Hi, we have an oil central heating system with a Worcester boiler. Our radiators were not getting very hot today and on checking the pressure gauge, it was on 0. I topped it up to 1.5 bar and over about 20 minutes it again went down to 0. Ive topped it up several times but it just keeps losing pressure. There is no air in any of the radiators and no leaks that we can see. There is no water coming out of the pipe outside. Anyone know what the issue could be? Thanks for reading.
 
You have a leak or it’s running down the condense pipe have you checked that ?
 
You have a leak or it’s running down the condense pipe have you checked that ?
Thanks so much for your reply. We have checked all the pipework and radiators and can see no leaks. The condense pipe goes into the soil pipe behind the utility cupboards so not easily accessible but I think that must be where it is going. There is no water under any of the units or around the boiler. What would be leaking for it to discharge into the condense pipe?
 
Main heat exchanger

Can you disconnect the condense to see if it’s running / dripping when your filling up etc ?

If not it’s under / in a floor somewhere
 

Reply to Heating loses all pressure over 20 minutes in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

I have been facing central heating low pressure on unvented hot water RM Cylinders but can't see any leak on the PRV, expansion vessels and plasterboard celling. I have got unvented pressurized RM Cylinders hot water system with 27KW Worchester gas boiler with expansion vessels . When...
Replies
2
Views
458
losing pressure
L
Can central heating / gas engineer expert help me with below issue. During winter time only, I have been having issue with low pressure or pressure dropping with unvented hot water cylinder system. During summer time there is no usage of central heating so the pressure at unvented system is not...
Replies
0
Views
576
Hi, Looking to see if anyone can give some advice please. My Baxi boiler has been losing pressure and I am having to top it up approx. every 4 hours from 0-1.5 bar each time. This has been going on a week now. I have also started to notice small drips running down my condensate pipe...
Replies
7
Views
738
the pressure of my boiler looks unstable After i re-pressurize to 1.5 bar, using tap is ok without problem. but when turn on the central heating, the pressure rises over 2 and the error code 117 showing water pressure high After i did the bleeding and re-pressurize to 1.3 bar, the heating is...
Replies
0
Views
380
Hi, Over the past few months, my wife and I have noticed a constant pulsing sound throughout the house which is particularly noisy at night (this could be as a result of us noticing the sound more when there is less environmental noise). Unfortunately, it is severely disrupting our sleep, so we...
Replies
4
Views
628
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock