I have a Grundfos UPS2 fitted and its become very loud humming when heating comes on, airing cupboard outside bedroom so not ideal
It stops after 15mins as the waters warmed up so my thinking is the pumps on its way out?

When fitting the Grundfos UPS3 are people leaving it on the factory setting III or are we putting it back to the II as we did with the UPS2, not keen on keeping using the moduaoting flow on the new pump as seems daft with a modulating boiler

my system is a unvented system with boiler and tank

Thanks in advance
 
Speed 3 on that pump would be overkill for any normal system as its 6.5M, even speed 2 at 5.2M is very powerful, speed1 at 4.2M should be satisfactory IMO, reason being that the pump still runs in a constant pressure fashion for some of the flow requirements, not like real (old) fixed speed pumps.
Constant pressure CP1 at 3M should be a good choice.

It is recommended to run on speed3 for is it 10 mins? to vent air from the pump.
 
You can see the pump curves/output here.

1610723914077.png
 
Speed 3 on that pump would be overkill for any normal system as its 6.5M, even speed 2 at 5.2M is very powerful, speed1 at 4.2M should be satisfactory IMO, reason being that the pump still runs in a constant pressure fashion for some of the flow requirements, not like real (old) fixed speed pumps.
Constant pressure CP1 at 3M should be a good choice.

It is recommended to run on speed3 for is it 10 mins? to vent air from the pump.
That's great thank you, I will run it at setting 2 and see how it goes, do you agree the pump needs replacing with it humming loudly until it gets warm and then stops bene loud?

the system is a new build so 22mm manifolds with 10mm to all the radiators
 
If it’s working I would just buy a pump to swap when it goes
 
My only issue is the airing cupboard is outside baby's bedroom and hums and vibrates very loud when starting up until it gets warm.
I have ordered the UPS3 and will set it at setting 2 and hope it sorts the noise out
 
I have replaced my old UPS 2 universal pump with a UPS 3. Although when the central heating is on (pump setting 1) the system works find but when i put the hot water on with or without heating i have air gussying around the system and there seams to be a little "back pressure" and when i shut the hot water off i need to bleed some radiators. this as resulted in that i have to rely on my immersion heater for hot water.
p s never had this problem before changing the pump.
Would be grateful for any advice
 
Presume OV system, the UPS3 is a very powerful pump even on speed 1, any idea on what speed setting the UPS2 was on?.
I would suggest changing from pump setting 1 which is 4.1M to constant speed 1 (CP1) which is 3M, this may cure your problem and still give adequate flow rates.

Also ensure the pump has been installed correctly orientated.
 
Last edited:

Reply to Grundfos UPS2 for UPS3 in the USA area at PlumbersForums.net

Similar plumbing topics

I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
137
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
310
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
4
Views
390
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
82
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock