Horizontal and vertical flues

Existing installations no clips on extensions definitely AR? Or defect? Bit of a grey area, also self tapper screws? Ar or defect? If flue has neither but is solid would you leave on?
 
See GS(IU)R 27 and 28 - it is not a grey area, the regulations are very prescriptive.

If there is any leakage of Products of Combustion (POC) from the flue joints, appliance or condensate air break - it is ID

If there is no leakage of POC:

Insecure or inadequately supported flue it is AR

Incorrect jointing methods of the flue, screws missing or inappropriate lubricant used on push fittings it is AR
 
Last edited:
See GS(IU)R 27 and 28 - it is not a grey area, the regulations are very prescriptive.

If there is any leakage of Products of Combustion (POC) from the flue joints, appliance or condensate air break - it is ID

If there is no leakage of POC:

Insecure or inadequately supported flue it is AR

Incorrect jointing methods of the flue, screws missing or inappropriate lubricant used on push fittings it is AR
So if you had a terminal not 300mm from an openable window but less, but no POC was entering the property, would you class as defect or ID? Im hearing lots of opinions recently
 
So two parts of the GS(IU)R to consider:

Non- Compliant Terminal position is covered by regulation 27 would be AR, provided always that products of combustion (poc) are not entering the building.

The process for the Assessment of the Risks for poc to re-enter a building are set out in Gas Safe Technical Bulletin TB007.

So, the answer to your point for the terminal you described is AR. However, you would need to be satisfied and to be able to demonstrate that the requirements of TB007 had been taken into account, in making your decision, in the event of any subsequent issues.

Obviously if poc are re-entering the building, then it is ID.
 
Last edited:
So if you had a terminal not 300mm from an openable window but less, but no POC was entering the property, would you class as defect or ID? Im hearing lots of opinions recently

Ar I would class it as
 
So two parts of the GS(IU)R to consider:

Non- Compliant Terminal position is covered by regulation 27 would be AR, provided always that products of combustion (poc) are not entering the building.

The process for the Assessment of the Risks for poc to re-enter a building are set out in Gas Safe Technical Bulletin TB007.

So, the answer to your point for the terminal you described is AR. However, you would need to be satisfied and to be able to demonstrate that the requirements of TB007 had been taken into account, in making your decision, in the event of any subsequent issues.

Obviously if poc are re-entering the building, then it is ID.
Thanks for clearing that up bud
 

Reply to Flues (AR and ID) would like to lnow what fellow gas engineers think of this grey area in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

Hi, My current hot water system needs to be replaced. Anyone got any suggestions or can recommend any plumbers around Derrimut area that won't rip me off? An office guy recommended me to apply for government rebates and get it installed through timetosave.com.au. How reliable is this...
Replies
6
Views
277
My son has an apprenticeship interview for to become a plumber and heating engineer. The have said there will be a multiple choice exam for this for suitability. The thing is my son panics during tests/exams. Is there any book I can buy him to practice the multiple choice test for the exam? What...
Replies
3
Views
400
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
234
Our kitchen mixer tap has started dripping. Like so much of the plumbing in our almost new build bungalow, it is lacking! The plumber didn't install any isolating cocks in the H&C feed to the tap so how can I identify which of the valves is passing? Shut the whole H&C water system down?
Replies
12
Views
314
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
310
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock