We have a gas boiler in the kitchen downstairs, and the 22mm feed and return go across the ceiling (in the joists) to the airing cupboard where the pump and valve (diverter valve for CH and HW) are. Between the boiler and pump the 22mm passes under our bathroom, and I would like to fit a towel radiator there (so it would heat when either the CH or DHW are demanding heat from the boiler) . . .
. . . but can I tap into the 22mm feed and return BETWEEN the boiler and the pump? Or will that just not work? Do I have to run a feed from the airing cupboard after the pump?
Thanks for any suggestions.
Robert
 
Hi
You will need to tee in after the pump. Won't work otherwise. The return can be joined into the main run.
The rad will then be on whenever the boiler fires.
 
Status
Not open for further replies.

Reply to Fitting a towel radiator between the boiler and pump? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
422
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
540
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock