M mickeyuk Messages 48 Dec 13, 2010 #1 Hi iv just fitted a Worcester 24i junior and the gas rate of 2.59/m3h seems a bit high to me.
B Billy Bob Bob Dec 13, 2010 #2 seems fine to me when you consider that most 30kw will pan out at 3.22
B Billy Bob Bob Dec 13, 2010 #6 no have you worked it out on input,as i dont fit worcesters i dont know what service mode is its probably were the boiler would be set to carry out a fga
no have you worked it out on input,as i dont fit worcesters i dont know what service mode is its probably were the boiler would be set to carry out a fga
M mickeyuk Messages 48 Dec 13, 2010 #7 on the phone to Worcester when commissioning boiler every thing ok ? The only thing i can think of is his explanation of gross to nett
on the phone to Worcester when commissioning boiler every thing ok ? The only thing i can think of is his explanation of gross to nett
B Billy Bob Bob Dec 13, 2010 #8 if its been worked out as input and come up as 27.8 kw its normal for a 24kw combi