T

timmytank

Hi I am hoping for some help please. I am newly qualified to unvented and did my g3 about 10 weeks ago. I am gas registered not that this matters.
I have corrected some issues with a rointe electric unvented cylinder in an apartment...sorted the balanced cold ,new expansion vessel sized correctly and I have piped up the d1 and d2 pipe in copper. It is 8.8 meters including 4 bends at 0.8. The fall is correct and 300mm between the tundish and bend. It terminates in to a metal hopper high level and building control have okayed this.
The problem is I was called today with a leak ..I watched in horror on a video he had taken as it disharged violently into the d2 and overflow the tundish. This would mean the d2 is not correct but it was within the 9 metres allowed. I have checked the that the main is 3 bar after the pressure reducing set and have checked the new expansion vessel is at the manufacturers 3bar. So the the temperature relief valve has gone off and rointe have been useless. The customer said a further 3 of these units in the block have done a similar think and they only use them for an hour a day . These unites have an anti leiganella programmer so they go up to 80 degrees once a day. The system has worked as it should since the alterations but the unit is 5 years old.
Any advice please would be helpful.
 
only needs to hit 60 degrees to control the risk so proably getting too hot
 
Thanks lame plumber I suspect high limit stat has failed. My other worry was the d2 pipe...even though it was 22mm and less than 9 metres including the 0.8 allowed from each bend it spilled over. Have you ever heard of this...it came out with a massive force.
 
No Scott_d definitely not. Appreciate your help. Not sure what to do.
 
It is not unusual for them to overflow / splash a bit when they discharge even if all the discharge pipework is correctly sized & installed.

It is the fact that it is discharging under temperature that needs your attention as you are no doubt aware the T&P is preset to discharge full bore if the water temp reaches 90-95degC & it is the last line of defence as it were so there must be a problem with the control & high limit stats.

If it has been regularly up to those high temps & you are in a hard water area then I would also be checking for scale build up on the sensors / probes or in the heater, as well as maybe replacing the stats.
 
Great thanks . I have talked to the customer and we are going to replace the cylinder. I had a call today from someone in the same block who has this problem and will be looking to change there's aswell. There are a further 3 with the problem....the problem is as I am new to electric unvented what is a reliable brand and I need to find out if I can put a scale inhibitor on these appliances. Thanks.
 
Most are stainless steel & so long as the temperature is controlled at 60 - 65 there will not be a problem with scale.

What type of scale inhibitor ?

Megaflo are good but expensive
 
Just be careful where you install the discharge pipe to that it can't back up. Check it all out. You said it goes to a hopper, but I know a gulley drain, if partly or fully blocked will cause the discharge pipe to be blocked, despite the regs asking for ideal situation of D2 terminating just below gulley grid.
Those tundishs are terrible for letting water splash out. Strange design
 
Last edited:
Thanks Chris Watkins. I had thought maybe an electrolyte scale inhibitor on the cold feed . I would check with the manufacturer first but the main is well over 200 ppm. I put these on my combis regardless.
I will price up a mega flow. Out of interest have you heard of telford or rather are they any good?
 
Thanks Best it's high level disharged into a metal hopper .. I had spoke to building control before doing this. It's definitely empty...I was just shocked how much spilled over.
 
Thanks Chris Watkins. I had thought maybe an electrolyte scale inhibitor on the cold feed . I would check with the manufacturer first but the main is well over 200 ppm. I put these on my combis regardless.
I will price up a mega flow. Out of interest have you heard of telford or rather are they any good?

IMHO those electrical or magnetic water conditioners are a waste of time & money, they may help a bit on your combi because of the slower water flows & instant use but not on an un-vented cylinder with the stored water & high surface temperatures of the immersions elements.

Scale will form on the element surface but break off & fall to the bottom of the cylinder due to the expansion & contraction. So long as it does not build up from the bottom & touch the element it will be fine, the key is the temperature is controlled to 60 - 65 Max.

Personally I would use Titanium Immersion Elements as these have proven to last 7+ years (in Megaflo's) working 365 for 4-5 hours/ night.
 
Just be careful where you install the discharge pipe to that it can't back up. Check it all out. You said it goes to a hopper, but I know a gulley drain, if partly or fully blocked will cause the discharge pipe to be blocked, despite the regs asking for ideal situation of D2 terminating just below gulley grid.
Those tundishs are terrible for letting water splash out. Strange design

I never understood that one either of discharging below the grating. I always suggested up to 50mm above, as it also give another point of warning if there is discharge guess it is the balance between splashing if it discharges full bore.

Also strange that the guidance for discharging at high level over a hopper (head) is that there should be an AA air gap between the down pointing D2 & overspill.
 
20160310_094120.jpg..20160119_110916.jpg
These are before and after...I havnt got a picture of the d2 termination because it was about 5 flights up. If really needed I could go back .
Thanks for your help Scott.
 
Lol at the before
If you have a longer section of straight pipe into the tundish it won't splash out so much. If space allows try ang get 150mm
 
As above ^^^, I would try to always fit the combination valve as high as possible - ideally just above the height of unit (if that is suitable). That means the combination valve is easy to service without draining any of the unit in future.
It also means you have plenty of height from the pressure relief valve and you could install the tundish higher, giving a decent straight length of D1 pipe (but D1 still within 600mm) and as long as possible straight D2 pipe before it bends. The 300mm rule on D2 before first bend is a minimum length and I try to better it greatly
 
Thanks alot. I will try and find the tap to the incoming main and move the combination valve up on the new install. Really helpful all of you.
 
Hi everyone I am looking in to replacing this rointe cylinder. I have been looking at a megaflo eco 210 unvented direct cylinder. I have spoken to megaflo and they said it is ok to use as electric only. Comes as a pack and has an internal expansion section.
My question is how do I register this gas safe don't want to know because there isn't any gas involved .....building control havnt shown much interest. I don't want to fit a new appliance and be in a position were I can't register. Thanks for any advice.
 
Are you Gas Safe registered ? If not then you or the customer need to raise a Building Notice.
Unless you want to join another competent persons scheme.
 
Last edited:
Yes I am gas registered . I spoke to my area gas safe inspector and he said I could register but as soon as I told him it was electric only he said that it wasn't possible. I logged on to gas safe register and couldn't find anything either.
 
Lacb I think might be the only way unless anyone can recommend cps scheme I could join. What a pain haha.
 
Should just be able to add it on to your gas safe same as I did with my oftec. You can join any cps that recognises your award. I wouldnt use megaflow, overpriced. If you want them then use the plumb center own brand made by same people. I like the rm's.

Sounds like you could be spending a bit of time in that block :)
 
Honestly not many the way this is going...maybe 10. I will try and stick to the boilers but some times you get a job kind of pushed your way. What are your thoughts?
 
Thanks SimonG . I think you could be right they are really badly installed, I wish my name hadn't been put forward. I did look at the centre option and it was 300 quid cheeper...also a dimplex . The dimple comes with a built in programmer. Had a great week last week ,update an old y plan to a combi, shower replacement and some taps and this is been on the back of my mind. Haha
 
Fitted pre plumbed megaflow, centerstores, RMs, warmflows, gledhill.

Megaflow overpriced, warmflow needs compression fittings for all the connectors. Stopped fitting the center ones asI dont use plumb center much. RMs I either get from my local merchants or Williams. Local is slightly cheaper.
 
I never understood that one either of discharging below the grating. I always suggested up to 50mm above, as it also give another point of warning if there is discharge guess it is the balance between splashing if it discharges full bore.

Also strange that the guidance for discharging at high level over a hopper (head) is that there should be an AA air gap between the down pointing D2 & overspill.

I always put it down to a floor gully grid can block with leaves/litter etc, so with the pipe discharging under it, there shouldn't be a problem (fine in theory, not in practise)
And even if a hopper blocks, if your pipe is 50mm above it, it shouldn't be affected by it
 
Unvented can be added to gas safe card

Provided it's connected to a gas appliance they would let me register it. Electric on its own there not interested...I'm still stuck any suggestions.
 
Just ask the customers to raise a Building Notice with there local Building control office it will cost them but you do not need to get involved apart from providing your unvented details.

Tell them that your price is lower to reflect this.
 
Just thought I would let you know how it was going...labc have told me they want me to register it with competent workers scheme. I told him that gas safe didn't want to deal with it , so they said my sparky can register it through niec and put a sub note with my g3 qualifications etc. He then told me I have to endelible mark the cylinder with my credentials. It seems like this is the only way....he has heard of the property I am at before and it's been a nightmare.

Then last week someone from another apartment rang me with issues but the problem is its grade 2 listed. This means I come up with issues on the d2 as the original d2 is shocking. I will upload a picture shortly. The only thing I can thing of is to upscale a new d2 to 28mm and run it to the ground from the first floor and put a cage around the bottom and lag it with armaflex. (Advice on this would be appreciated )..
 
2016-04-05 22.41.46.jpg This is the d2 in the other property. There are another 8 of these I will have to quote for.. the ones in the basement will be screwed and I'm not getting g involved
 
Why would you lag the D2 pipe?
I would be concerned about copper (if used) D2 pipe being stolen at apartments if easily got at.
Ideally the D2 is supposed to be fitted into a gulley, or if above it, or above bare ground, it needs to be max of 100mm up and you need a cage there to prevent someone getting too close to hot water.
 
Thanks Best , there is a gully with a cast drainpipe that terminates above it. My plane was to run it to the side of the gully and armaflex it to disguise it. Thinking about it as you have pointed out this may well be discovered and stolen. I could cut into the cast and put another hopper in line and terminate the d2 in this. I will have to check with the listing people.
 
Status
Not open for further replies.

Reply to Electric unvented cylinder help. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
245
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
145
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
220
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
359
I want to reconnect some outbuildings to an existing water supply. The supply pipe is old 22mm MDPE and buried for a fair distance so not going to dig it up and replace it 😬. Question is can I use normal 22mm plumbing push-fit connectors to make the connection as finding 22mm MDPE fittings...
Replies
1
Views
277
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock