hi guys, pressure had zeroed so topped up pressure. Boiler still flashes ea code, when you reset the boiler you can hear the electrodes trying to spark.
I'm going back tomorrow my plan is to do a gas pressure test on the inlet. If there's no pressure ill remove gas valve and see if there's any crap inside it that's restricting the gas flow.

Any other checks you experienced guys would recommend?
 
Bearning plate, electrodes etc tbh depending on electrodes state full service recommend

16020EE9-F1B2-4C30-AADC-ECCB61741C3E.jpeg


E8641C6C-A3DA-4559-9861-632389734463.jpeg


5D43E230-CA24-4E5D-8F0C-AF3952B98B9B.jpeg
 
End figures for the above 9.6 and 60ppm
 
Hi guys from testing the boiler the gas valve doesn't seem to be opening up. I placed a guage on the inlet gas valve and turn off the gas cock on the boiler and when started the boiler and the pressure stayed the same while the boiler was trying to fire but never did.. fan works then electrodes are trying to spark. I removed the gas valve a white flakes debre was removed. If it was the bearing flap wouldn't the fan stop working?
 
If your not registering a drop on the gas valve with the iso off need to see if it’s getting power if yes gas valve
 
If your not registering a drop on the gas valve with the iso off need to see if it’s getting power if yes gas valve
Hi Shaun, I went to the boiler today with a sparky, before he arrived I reset the boiler then turned the power off, then the boiler fired up? Fga readings are good. Strange?! Im going back on Monday to finish off the boiler service.
 
Could be one of those intermittent faults
 

Reply to Ea fault code Worcester cdi in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Morco feb 24ed3 has a f1 fault code. The burner reading is fine. The fault is intermittent, sometimes the boiler won't ignite on either hot water...
Replies
0
Views
514
Hello Wondering if anyone can offer any clues please // Potterton Promax 18 // Had an E1 error code, repressurised via with filling loop //...
Replies
1
Views
305
Hi all. I hope you are well. Need some advice on this boiler and fault. E229. Went there and condensate was totally blocked so cleaned it and...
Replies
0
Views
372
Hi, I am handy DIYer but not interested in touching anything boiler related! Just interested before I get a Gas safe engineer out what I could be...
Replies
3
Views
2K
Just been to a nightmare of a job! Had to carry out a service on the 2009 British Gas 330 + (GC: 41-019-11) It's a Glow Worm boiler. The boiler...
Replies
11
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock