Discuss C plan system airlock in the Central Heating Forum area at PlumbersForums.net

S

Sam Grocock

Hi guys, we moved into a place last Dec with an old Grant Euroflame oil boiler with 4 pipes, one set with a Grundfos pump on it and the other set running upstairs to a HW cylinder. We've never been able to get HW generated from the boiler for a sustained period, the water doesn't seem to flow that side at all.

Early this year I was having to regularly bleed the pump (which was 20 years old+) as the CH would get stuck and only come back after bleeding air from the old pump. I figured the pump was on its way out. A month ago I went to switch it on after it being off all summer and it wouldn't budge at all so we fitted a new UPS3 and it worked faultlessly for 2 weeks.

Then I partially drained the system down to add inhibitor, topped back up and since then after ~20mins of boiler+pump being on (doesn't happen if just the pump is running without the boiler.. even if the CH water is still running hot) there's a wooshing/gurgling noise and the pump will sound strained and the rads just cut off, no circulation. The pump goes dead quiet but still struggling doing something.

I've bled all the rads and there's no more air that I can get out, after getting some initially after the system was topped back up. When the block happens I have to turn the pump off and on for 5-10mins which is noisy (like bubbles going through it) and gets something moving and then the system will work for 10-20mins again. I've tried to bleed the rads closest to the boiler after the system is unblocked though, can't get anything out of them except water (which is clear, no sludge coming out). It's odd that the system was working just fine for weeks until I drained and topped it up.

Anyone with any similar issues in the past? Been wracking my brain for weeks to figure this out. Cheers.
 

Reply to C plan system airlock in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
207
P
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
140
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
213
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
481
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock