Pump some food colouring in the heating system via the filling loop if its shows up in the hotwater then bingo flush out do repairs . cheers kop

cheers kop. done it... but we are pressure testing the ch loop till wednesday, so if no drop from 2bar we will open up the flow and return and run the system... hope to see yellow hot water :)
I take it that if the engineer had the boiler open and tested it cold he would not see if the heat exchanger is faulty ???
 
Can you loose pressure through an unvented coil from a sealed CH system? I always thought the pressure on the main side of the cylinder being 3bar would if anything over pressurise the CH system an discharge via the PRV as the CH system pressure would only be around 1-1.5 as opposed the 3-3.5 in the cylinder? I'm genuinely curious as I would like to know if I'm wrong no discredit to other people's suggestions
 
Can you loose pressure through an unvented coil from a sealed CH system? I always thought the pressure on the main side of the cylinder being 3bar would if anything over pressurise the CH system an discharge via the PRV as the CH system pressure would only be around 1-1.5 as opposed the 3-3.5 in the cylinder? I'm genuinely curious as I would like to know if I'm wrong no discredit to other people's suggestions

Your reasoning is correct.

However, it wasn't clear from the original post whether the system was vented or unvented and it's easy to miss such details when they are buried in a thread of more than 30 posts.
 
Can you loose pressure through an unvented coil from a sealed CH system? I always thought the pressure on the main side of the cylinder being 3bar would if anything over pressurise the CH system an discharge via the PRV as the CH system pressure would only be around 1-1.5 as opposed the 3-3.5 in the cylinder? I'm genuinely curious as I would like to know if I'm wrong no discredit to other people's suggestions

Yeah it's a fair shout. But what your talking about there is static pressure. As soon as you open a tap now you've dynamic pressure, which is less by about half.
So when you open a hot tap you may see the boiler pressure (heating circuit) fall and then when the hot tap is closed you may see the boiler pressure rise :)
 
Your reasoning is correct.

However, it wasn't clear from the original post whether the system was vented or unvented and it's easy to miss such details when they are buried in a thread of more than 30 posts.
I weren't meaning to sound rude,I was more worried I didn't know something that more experienced guys did. It was the OP's pic with the cylinder an the potable water expansion vessel with the PRV terminating into some sort of plant pot that made me assume it was unvented.
 
Yeah it's a fair shout. But what your talking about there is static pressure. As soon as you open a tap now you've dynamic pressure, which is less by about half.
So when you open a hot tap you may see the boiler pressure (heating circuit) fall and then when the hot tap is closed you may see the boiler pressure rise :)
cheers Dan, I wouldn't of even thought of that. I'm new to this an still gaining experience but thanks for explaining
 
Status
Not open for further replies.

Reply to boiler losing pressure - ch pipes not leaking. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no...
Replies
6
Views
279
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
296
PSxxxxxx
P
I have been facing central heating low pressure on unvented hot water RM Cylinders but can't see any leak on the PRV, expansion vessels and...
Replies
2
Views
506
losing pressure
L
Hi, Looking to see if anyone can give some advice please. My Baxi boiler has been losing pressure and I am having to top it up approx. every 4...
Replies
7
Views
785
Can central heating / gas engineer expert help me with below issue. During winter time only, I have been having issue with low pressure or...
Replies
0
Views
606