G

gymdad

just changed expansion vessel and prv to solve an increase of pressure, filling loop not by passing but pressure is still increasing even c/h is off could this be main heat exchanger
 
if you have ruled out ev,prv,and filling loop your plate heats pinholed
 
Turn off cold feed to boiler, if pressure stops increasing then gas man is probably right, plate to plate pin holed.
 
Either the plate to plate has pinholed or the pipe coming out of the bottom of the expansion vessel is blocked (quite common)
 
If the pipe is blocked, the prv normally blows off. water has no where else to go.
 
If the pipe is blocked, the prv normally blows off. water has no where else to go.
yes it will... eventually, but it will eventually if the plate to plate pinholes, changed one 2 days ago for same thing. It doesn't have to be a catastrophic blow off, it sometimes releases as a constant slow flow / drip
 
Status
Not open for further replies.

Reply to baxi 105e in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have a green star ten yrs old keeps increasing pressure, feel on off filling valve not working, drain off to recommended, but after few days it's increased whilst cold...is this a regular problem.
Replies
1
Views
146
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
139
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
231
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
243
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock