I currently have a 20 year old 24kW thermocompact system boiler which is costing a fortune to run.

I have 13 radiators, hive TRVs and a total heat loss of 7kW, my unvented cylinder takes 17.2kW to recharge.

The boiler I’m looking at is an Ideal Vouge Max, would the advice be to err on caution and go for the 26kW version accepting it will modulate down to 3.7kW but still oversized for DHW, or go for the 18kW version as this meets the load but with not a lot left in the tank.

Thanks
 
18kw or 12kw as your load is 7kw will take an extra 30 mins ish to heat the hot water etc
 
18kw or 12kw as your load is 7kw will take an extra 30 mins ish to heat the hot water etc


Agree. Loads of boilers are oversized, then you find out the gas pipe is too small.

I had a job in a flat where a new boiler was installed. 6 radiators and roughly a 200L unvented tank.

The new boiler was 30kw+, it was sucking the gas pipe dry. It was either in grade the gas pipe (scaffolding and knocking holes everywhere), or swap the boiler out.

Put a 12kw in, its now sized correctly for the gas pipe and the properties demand. The heating/hot water work perfectly.

Typically, if the system is balanced/return temp correct for condensing, the longer the boiler stays on, the better for efficiency.
 

Reply to 18kW or 26kW - higher or lower says Brucie in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi everyone, I'm looking for some advice please. My system has 5 Drayton Wiser TRVs. There are 8 rads over 3 storeys and a 170l unvented...
Replies
10
Views
2K
Hi there, thanks for your time to look at this record long post!! I work on the operational management side or a small building contracting firm...
Replies
9
Views
1K
H
Hi there, thanks for your time to look at this record long post!! I work on the operational management side or a small building contracting firm...
Replies
0
Views
655
HRP123
H
R
  • Locked
Hey all, apologies for the long post: I've had a new Ideal Vogue boiler installed with a T6 wired thermostat so the OpenTherm is activated as...
Replies
0
Views
4K
richardc1983
R
N
  • Locked
Hi All, I just wrote a long post and then suddenly lost it when it came up to submit it .. :disappointed: So here goes again, but a lite version...
Replies
85
Views
22K
Back
Top