5 Storey Victorian house, Boiler in the basement. It's actually 13.5M, (I measured it exactly) so 15M being the closest.
Discuss 15M pump required, one large Vs 2 small in series? in the Plumbing Jobs | The Job-board area at PlumbersForums.net
5 Storey Victorian house, Boiler in the basement. It's actually 13.5M, (I measured it exactly) so 15M being the closest.
If you are talking about a circulation pump, it doesn't need to have a head of 13.5m, which is what you seem to be thinking. This is because the inlet pressure is 13.5m and the outlet pressure is the sum of the pump-inlet plus pump-working pressures. So you only need enough head to overcome the impedance of the pipework, which should be sized to work with a standard 6m pump.
Yes it's a circulation pump, in a sealed system. Will have Worchester Bosch 40CDi Classic with a Robo kit. I get your point if it were open vent, or am I missing the point?
unvented cylinder?
i would say your shy on your heat loss calcs
unvented cylinders require 15-20kw on there own
If you are talking about a circulation pump, it doesn't need to have a head of 13.5m, which is what you seem to be thinking. This is because the inlet pressure is 13.5m and the outlet pressure is the sum of the pump-inlet plus pump-working pressures. So you only need enough head to overcome the impedance of the pipework, which should be sized to work with a standard 6m pump.
Cylinder is 20kW, Radiators are 17kW.
Yes it's a circulation pump, in a sealed system. Will have Worchester Bosch 40CDi Classic with a Robo kit. I get your point if it were open vent, or am I missing the point?