1) gas piping has no earth bonding
2)redundant gas pipes have been left uncapped
3) boiler flue cut too short
4)flue terminal discharges to close to internal wall
5)flue terminal located within 25mm of a frame or opening into building should be no nearer than a frame of 150 mm if closed
6)no notification of install or boiler to relevant of building control authority
7)clearance of boiler insufficient from top of compartment
8) flue has pe nitrated load bearing element of building
9) 13 amp fuse fitted , should be 3 amp as MI
10)benchmark book not completed or even started , nothing filled in
11)external pipes uninsulated
12)condensate pipe not discharging below ground level or in drain ( discharging on wall and foundation)
13)condensate pipe too small only 22mm should be 32mm
14)new circulating pipework situated within boiler compartment has no insulation
15) incorrect power wire used for spur to boiler supply

+ many many more other points they have noted inc but not the end of the list

Inc bare wires under boiler
loose cables
boiler unsecure to wall
no electrical certificate for connections made
damage to carpets
damage to ceiling
unfinished pipework
unsecure radiators

and more.......
 
strange i would have put an unsecured boiler at the top of any list if it falls of the wall it is possibly catastrophic
and my pet hate the 13 amp fuse
 
my two pet hates

11)external pipes uninsulated
12)condensate pipe not discharging below ground level or in drain ( discharging on wall and foundation)

note they havent mentioned "no self tap in screws in the flue," they must have done them, that means they couldnt have been that bad (or maybe inspector just ran out of room)
 
Last edited:
There was more points noted , I would have just copied and pasted but it's a pdf an I can't post it as it names the company involved
 
Thanks for all the updates Shaun. The stress must be taking its toll by now. I hope you get things resolved. Please be aware we're not all like this!
 
Item 6 is the only one that doesn't worry me. It's standard practice not to notify until final payment has been made.

The rest is inexcusable.....
 
Item 6 is the only one that doesn't worry me. It's standard practice not to notify until final payment has been made.

The rest is inexcusable.....

I also don't fill out the benchmark until the very last thing.
 
cc16bf26fc45a525aa370c0bcc6c3224.jpg

74391dfeb68f441f87087b7da4276465.jpg


Just seen the photo bucket link.
Just curious it looks like that isnt keyed into the brickwork ???
Hard to tell
 
Just read from first to last post. I have to say sorry Shaun once again for the few so called "tradesmen" who give the genuine decent ones the good reason to to say we are not all in the same boat. Going back to the lintel is it a steel one,concrete etc because I only ask as I caught the end a steel one once while coring (went a lot further than should have done) and boy did I know I hit it. So we'll played to the cretin that went right through it. Looking at the state of the job that must have been the longest part!

once again Shaun I feel for yourself as I myself have had to go and put things right after so called tradesmen and I have heard the custards relief that they could finally put their minds at rest.
i just hope that you can do the same soon?
 
Thanks for all the updates Shaun. The stress must be taking its toll by now. I hope you get things resolved. Please be aware we're not all like this!
It is starting to get to me, I'll keep strong and fight them all of the way .
i know you are all not like them especially because of the support on here
th
anks again :)
 
cc16bf26fc45a525aa370c0bcc6c3224.jpg

74391dfeb68f441f87087b7da4276465.jpg


Just seen the photo bucket link.
Just curious it looks like that isnt keyed into the brickwork ???
Hard to tell

It goes all of the way into the wall , what looks like a gap on the bottom picture is actually some plaster board fitted to finish off the window ,
if you look closely on the first picture you will see the screw misses the plasterboard and goes straight into the internal wood lintel , follow the straight edge of that and you see it goes into the brickwork

cheers again
 
Last edited by a moderator:
strange i would have put an unsecured boiler at the top of any list if it falls of the wall it is possibly catastrophic
and my pet hate the 13 amp fuse
I don't think the list was in order of worst to best ( if you can call it that) mistakes but more just what he noted
 
shocking installation from start to finish! I would take photos and document everything. you have a gas safe report. so I would just crack on a get it sorted. I think best option is to brick up opening internally and externally. This will sort the lintel and boiler positioning out. its very poor work what they have done. but I wouldn't worry to much about the structural integrity of your house! you have no external lintel only a soldier course which the window itself is holding up. the internal lintel should be replaced though, but it will only effect possibly 3 to 4 courses of bricks in a triangle above the window as the brick work supports itself and its only a small window!
 
shocking installation from start to finish! I would take photos and document everything. you have a gas safe report. so I would just crack on a get it sorted. I think best option is to brick up opening internally and externally. This will sort the lintel and boiler positioning out. its very poor work what they have done. but I wouldn't worry to much about the structural integrity of your house! you have no external lintel only a soldier course which the window itself is holding up. the internal lintel should be replaced though, but it will only effect possibly 3 to 4 courses of bricks in a triangle above the window as the brick work supports itself and its only a small window!

Thats prettymuch exactly what has happend.
After gassafes report i sent them a mail giving 7 says to respond to me if they are interested in any further discussions so I don't take them to court ,, gassafes report stipulates they has 7 days to rectify the work also , I even spoke to their office yesterday to give them one last chance of discussions and said they had until midnight last night to come back to me to negotiate what they are going to do or fitters were coming in to strip everything out that they have done and the new installation and repairs will commence .

no contact from them so that's what's been going on today , I've took pics as they have been removing it and I've boxed it all up neatly down to the last copper bend , it will be all packaged up and returned to Sfs with a bill for removal as well as any damages I claim through court .

they still I think insist that they will be taking me to court for payment even though I don't have anything from them that I actually ordered + all of the issues and **** installation on top of that is beyond belief that they think they have a leg to stand on
 
Good luck I hope you get what you deserve without too much stress.

I find it dissapointing that even with all of todays self certification /competent person schemes for various trades some still feel they can provide a poor and in your instance a potentially dangerous service.

No pride and no shame and even self policing isnt enough to deter the act in the first place...
 
Last edited by a moderator:
I wouldnt worry about them taking you to court

As you have mentioned they are in breach of contract for carrying out work not of a reasonable standard contrary to the Supply of Goods and Services Act 1982.

You can argue you have lost faith in their work and given the delays you have already talked about you should get someone in and rectify all of their work ASAP. Any losses caused by their workmanship can then be pursued through the courts if they refuse to pay.

You could always re-use the boiler and aprts they have given you if you can.
 
I suspect this doesnt need to be said but you should be documenting the date and time of every bit of communication with them, no matter how small. You should be able to supply an accurate diary of events showing everything that was said and done.

If it gets to court this will be invaluable.
 
I wouldnt worry about them taking you to court

As you have mentioned they are in breach of contract for carrying out work not of a reasonable standard contrary to the Supply of Goods and Services Act 1982.

You can argue you have lost faith in their work and given the delays you have already talked about you should get someone in and rectify all of their work ASAP. Any losses caused by their workmanship can then be pursued through the courts if they refuse to pay.

You could always re-use the boiler and aprts they have given you if you can.

Sorry mo7 but wouldn`t advise using a single screw if it`s theirs, give everything back would be my view.
 
Sorry mo7 but wouldn`t advise using a single screw if it`s theirs, give everything back would be my view.
I have had the company redoing this today and tomorrow remove everything including screws ,clips, copper pipe , bends, even a blood covered flue ( they obviously cut themselves fitting it ) and even their bit of plywood . All waste pipes, thermostatic valves , actually everything I can think of
 
I suspect this doesnt need to be said but you should be documenting the date and time of every bit of communication with them, no matter how small. You should be able to supply an accurate diary of events showing everything that was said and done.

If it gets to court this will be invaluable.

I have been doing this also thanks though :) as soon as I realised I potentially had the issue I started to log everything , I also have email from them stating the boiler I ordered with a 7 year warranty , price , timescale etc..
Yet they still delivered and installed a alpha Eco with a 2 year
thanks
 
You should bear in mind though that you should mitigate your losses.

So if they bought a boiler and it can be re-used and you go and buy a brand new boiler the court may question why you did not re-use the original boiler (if it was still usebale). They may then decide to reduce any award by the difference.

I appreciate you probably don't trust using a boielr they have bodged - but you need to be able to argue it - and it depends on what the court thinks on the day.

I understand they bought the wrong boiler initally but you accepted the change.

I should add I am not a plumber but I do have experience of civil law/consumer rights legislation.

Also I don't actually know whether the original boiler was ruined of course.
 
You should bear in mind though that you should mitigate your losses.

So if they bought a boiler and it can be re-used and you go and buy a brand new boiler the court may question why you did not re-use the original boiler (if it was still usebale). They may then decide to reduce any award by the difference.

I appreciate you probably don't trust using a boielr they have bodged - but you need to be able to argue it - and it depends on what the court thinks on the day.

I understand they bought the wrong boiler initally but you accepted the change.

I should add I am not a plumber but I do have experience of civil law/consumer rights legislation.

Also I don't actually know whether the original boiler was ruined of course.

Ah great! The ruddy lawyers are getting involved already! :tounge_smile:
 
You should bear in mind though that you should mitigate your losses.

So if they bought a boiler and it can be re-used and you go and buy a brand new boiler the court may question why you did not re-use the original boiler (if it was still usebale). They may then decide to reduce any award by the difference.

I appreciate you probably don't trust using a boielr they have bodged - but you need to be able to argue it - and it depends on what the court thinks on the day.

I understand they bought the wrong boiler initally but you accepted the change.

I should add I am not a plumber but I do have experience of civil law/consumer rights legislation.

Also I don't actually know whether the original boiler was ruined of course.


I have never actually accepted the boiler from them , the boiler I ordered was totally different with a different warranty , they tried to scare me into saying that the alpha was far superior, I agreed to consider it but insisted I would only accept if the could confirm in black and white that they would give me a 7 year manufactures warranty .
the boiler I have quotes for was never delivered .

to this day they have still not provided me with this and they can't either . They were offering a 7 year warranty through the company and not the manufacturer , I explained this was not acceptable as if the company goes bust in a year or two then their 7year warranty is usless .

i offered to purchase all parts from them origonal boiler and they walk away from any fitting work and they also refused this . They want and expect a full payment of just under ÂŁ3000 for the work they done .

ive decided now that every penny of my hard earned cash will go to a local fitter ,a hardworking someone who appreciates values , honesty and who deserves it .

Sfs don't deserve a penny from the work they carried out , the dishonesty , lies , thievery, ineptness, shabby work ,awful customer services to name a few , not a penny will go to them and I will gladly go through court if I need to .

I have all info , quotes , documents , emails , phone logs , calls, voice recordings , photos , recordings of them admitting they are in the wrong . And I guess I will just have to ride this one out .

i have considered contacting watchdog or other program's but I thought they would have handled it better , I might still go down this route , it should make for good viewing .
 
If they take you to court just counter sue them for damages
You will win
 
Woo hoo ,
I've got hot water
ive got heating .
Window lintels replaced
brickwork done
new boiler fitted neither alpha nor vokera
New pipework done neatly
everything removed from the origonal install .

Two great guys and their young apprentice local to me and both frequent the forum sorted it all out .
I will not name them but if they read this and want to post up then that's upto them .

The other company contacted to say they are free to collect their belongings from boiler down to the last screw when it's a convenient time for me and only once they sign a collection notice

As far as a completed job I am now a happy man and my wife will be even happier tonight now she can have a shower in her own house , the last one was over 1month ago .

i just now have to wait until they( other company ) decide would they still like to Persu me through court for payment .
and if so what happens with counter claims from my side

ive give them the option to walk away from this with nothing or go through court and I claim everything I can , I wont abuse it but I will claim , carpets , ceiling decoration ,money paid for replacing lintels, brickwork and removal of there system that I didn't order .
also loss of earnings for extra days I've had to take off etc..

i will keep you updated if things do develop but for now thanks again to everyone

happy Halloween
 
That's great your up n running, heating n hot water is taken for granted until we don't have it, I'm sure you've had a terrible time as the nights get colder , happy heating
 
That's brilliant Shaun, thanks for keeping us updated.

And I would love the UKPF Knight in shining armour to come forward and identify himself for the congratulations he richly deserves!
 
Glad to hear everything is up and running. What boiler have you now ended up with, hopefully not a ferroli lol
 
Glad to hear everything is up and running. What boiler have you now ended up with, hopefully not a ferroli lol

FERROLI what the hell is wrong with FERROLI? That's what I've got .........omg what the hell

just kidding , I was offered a few but bare in mind I was trying to stick within a budget of getting a system fitted for a second time as well as paying for correctional work so I had to have a think .
it wasn't the cheapest nor the most expensive option but it was my choice

i didn't want something I hadn't heard of again as I would fall into the vokera / alpha scenario of people saying I wouldn't have either , they are both crap :( lalalalalala

i wanted someting with a good warranty and after looking through review sites and which website I was finding good and bad review of almost every boiler under the sun I went with a baxi duotech 28he mk1 with a digi wireless thermostat control.
I think they have been around a long time and parts I'm sure are fine to get hold of and the warranty is 7 years

if its **** just don't tell me :) I'm happy with it lol
 
Last edited by a moderator:
Stand and be counted , whos spartacus

Hes spartacus and im ferroli lol
 
So who was it then who did the work.
No need to keep it quiet.
Im sure theyll bathe in the free publicity for years to come.

And can we have images of the new install inside and out !
 
FERROLI what the hell is wrong with FERROLI? That's what I've got .........omg what the hell

just kidding , I was offered a few but bare in mind I was trying to stick within a budget of getting a system fitted for a second time as well as paying for correctional work so I had to have a think .
it wasn't the cheapest nor the most expensive option but it was my choice

i didn't want something I hadn't heard of again as I would fall into the vokera / alpha scenario of people saying I wouldn't have either , they are both crap :( lalalalalala

i wanted someting with a good warranty and after looking through review sites and which website I was finding good and bad review of almost every boiler under the sun I went with a baxi duotech 28he mk1 with a digi wireless thermostat control.
I think they have been around a long time and parts I'm sure are fine to get hold of and the warranty is 7 years

if its **** just don't tell me :) I'm happy with it lol

I like the duotec good boilers.
 
So who was it then who did the work.
No need to keep it quiet.
Im sure theyll bathe in the free publicity for years to come.

And can we have images of the new install inside and out !

I don't know legally where I stand with naming so maybe I shouldn't for the time being . I've sent a email off to watchdog though just Incase ;)

All I could say is its SomeF--ingStupid homeassist company from the north east ;)

but I did take some pictures once the boiler was removed and during the repair work

there was 5 screws holding the boiler to the wall
2 through the lintel either side and two just into the top of the wood windowsill behind . 1 screw into the wall on just the right hand side but right into the corner so it wasn't holding , I've got some good pics of the lintel damage and replacement so when I get time I'll list it and put it up , you guys should have it available to upload straight from a iPhone
 
The NEW install lol


(Ive tracked down who did the bodge)
lol I do have some dull moments :)
Sorry a local company called WAVES and believe it or not he ends up being only a few streets away from me :) John came with a friend of his another gsr fitter and a young apprentice came too they all done the work and repairs. Fast clean and a pleasure to talk too

like I say though if they want to have input on here that's upto them but anyone looking for work in the northeast I would recommend them for sure ( as well as any other local fitter on this superb forum ;) ..)
 
So who was it then who did the work.
No need to keep it quiet.
Im sure theyll bathe in the free publicity for years to come.

And can we have images of the new install inside and out !

The individual in question wants to stay out of the lime light, we should respect their/his/her wishes. When they feel the need, they will raise their head out of the water and we will heap them with praise.
 
Can Shaun be a honorary member and now join us for a pint in the arms ???
 
Status
Not open for further replies.

Reply to Please HELP with new combi boiler , possible nightmare on my hands in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have a "Firebird Envirogreen Condensing Combi Oil Boiler 26kW" a part has went and I can't find it anywhere, I was at every plumbers merchant...
Replies
2
Views
434
Hi, Just had a "Main Eco Compact" combi boiler installed as the Biasi one failed. It seems to work fine, gives a hot bath, i dont ever use the...
Replies
2
Views
464
Hello, bit of a noob question but would someone be able to help me to understand the pipes coming off our boiler. It's a Grant oil combi boiler...
Replies
9
Views
721
My Grant combi oil boiler is giving me quite a headache at the moment. When I returned home last Friday I'd no heating or hot water. An engineer...
Replies
3
Views
609
M
I am currently in the middle of a complete rennovation of my house and need some advice on what kind of boiler to get. The house will have 4...
Replies
5
Views
744
Back
Top