Almost every Grant I attend has a leaking AAV, this one is on a Firebird. Changing them doesn't fix it, what do you do?

ImageUploadedByTapatalk1377677917.496321.jpg
 
If its a sealed system Usually to do with expansion vessel
Needs re charging or undersized
 
Normally mucky system. Recommend system is flushed.

If you disassemble Aav once removed normally find that muck trapped between top of float and lid of chamber or guide for float is mucky, thus when air has left system Aav isn't reseating properly. Think most Aav are tested to. 10 bar so prv should kick in before it fails?
 
Funnily enough, i posted the op while at work, the very next job was one of those 'services' where actually its a leak, kitchen roll soaking in base of boiler cab -

Custard: "can you fix while servicing?" -
Me: "No, lets fix the leak then see if there is time to service it..."
which there wasnt so they'll have to pay the call out.

Grant, another AAV - immediately after posting the above, how timely! Fortunately a gravity on a bungalow with idyllic loft access etc.
 
Heat seems to ruin them & cause them to leak.
If they are on a colder part of system they tend to last & last.
Sadly can't do much when they are screwed straight into top of boilers, - unless somebody knows of better types.
 
Vent air from system and then screw black plastic cap in. It wont leak then
 
Status
Not open for further replies.

Reply to AAVs - why do they fail so much? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Our kitchen mixer tap has started dripping. Like so much of the plumbing in our almost new build bungalow, it is lacking! The plumber didn't...
Replies
12
Views
433
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason...
Replies
3
Views
339
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
283
PSxxxxxx
P
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the...
Replies
5
Views
325
Show us your fanciest radiators you've installed! We would love to see them! I love this Milano vertical radiator in the kitchen space. What...
Replies
4
Views
285

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock