Discuss Open vent DHW - calculate recovery time in the Central Heating Forum area at PlumbersForums.net

Messages
58
What would be the heating time for this (indirect) vented cylinder? Rated coil = 14kw
Is it 96 litres x 4.2 specific weight x 40 (dT) ? How do I calculate the heating requirement of the boiler to heat this cylinder.
Secondly, they are simpler to install as opposed to unvented type but what are the advantages they have over their unvented cousins?
Thanks in advance for guidance.
 

Attachments

  • vented cylinder.png
    vented cylinder.png
    1 MB · Views: 21
Not sure but my old college books all say allow 3kw for the cylinder

They have no advantages over an unvented. You would only fit a vented one if you didn't have means of getting a relief pipe out, the plumbing in the house is Rubbish or the water pressure and flow are not adequate
 
to heat 96l at dt40 your coil is only 14kw so around the 20-25mins mark
 
eg

20mins x60 second =1200 seconds
4.2 x96x40 / 1200 = 13.4kw at 20 mins
 
Thank you both of you.
The coil rating is possibly based on a 80C boiler temperature and a flowrate of maybe 30LPM which may not be the normal running conditions so maybe average coil rating of 8 to 10kw, still only a problem if you are programming the reheat time, maybe allow say 30/35 minutes in the summer and 40/45 minutes in the winter.
 
The coil rating is possibly based on a 80C boiler temperature and a flowrate of maybe 30LPM which may not be the normal running conditions so maybe average coil rating of 8 to 10kw, still only a problem if you are programming the reheat time, maybe allow say 30/35 minutes in the summer and 40/45 minutes in the winter.
Thank you Sir.
 

Reply to Open vent DHW - calculate recovery time in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Is there a standard for the above?, ie primary flow rate, primary flow temperature, reheat time from X degC to Y degC, continuous flow rates at...
Replies
0
Views
546
Hi there, thanks for your time to look at this record long post!! I work on the operational management side or a small building contracting firm...
Replies
9
Views
1K
H
Hi there, thanks for your time to look at this record long post!! I work on the operational management side or a small building contracting firm...
Replies
0
Views
653
HRP123
H
Hello I had a solar thermal installation. However, the Gledhill Stainless Steel Lite keepings making popping noises. Anyway, I was looking to...
Replies
4
Views
3K
Hi, After a bit of a saga with my plumber, I need to chose boiler size as soon as possible, the plumber is not going to do any heat loss...
Replies
16
Views
3K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock