Hopefully someone can help me out - the pressure reading on my boiler and in the hot press seems too high. Just wondering how can this be adjusted?


Hot Press:
image_67174657.JPG
image_67218689.JPG

image_67170049.JPG



Downstairs boiler:
image_67172097.JPG


image_67136257.JPG



Any help would be greatly appreciated
 
atag Q25S - Maybe I'm wrong in what I said. I have some water coming out of the pressure relief valve on the boiler so assumed the pressure is the issue
Ok, yes, that’s a system boiler, which does use pressure, and 2.9 is high, and prv seeping water is a telltale sign. So if it’s only high when the heating has been on for 10 minutes or so, and then returns to a ”normal” pressure or loses pressure altogether, then you have an expansion/possible prv fault. If it’s high without the heating being on, then it’s been over pressurised. If it’s the latter, you could drain some water from a radiator, ensuring, that the filling loop is closed.
 
It looks possibly the top PRV (pressure reducing valve) is the supply to the boiler (topping up) If just shut the red lever valve and the boiler pressure will/should fall, this PRV should be set to 1.5 bar and only opened if the boiler pressure falls to ~ 1 bar cold.
Can you take a close up of the Wilo Fluid Control pump before closing anything.
 
Ok, yes, that’s a system boiler, which does use pressure, and 2.9 is high, and prv seeping water is a telltale sign. So if it’s only high when the heating has been on for 10 minutes or so, and then returns to a ”normal” pressure or loses pressure altogether, then you have an expansion/possible prv fault. If it’s high without the heating being on, then it’s been over pressurised. If it’s the latter, you could drain some water from a radiator, ensuring, that the filling loop is closed.

The pressure is high without heating. I spent yesterday trying to do this but without success, when draining the pressure goes down but then fills back up when stopped. I tried finding a filling loop but couldn't, also have a water tank in my attic if that gives you any further information.
 
It looks possibly the top PRV (pressure reducing valve) is the supply to the boiler (topping up) If just shut the red lever valve and the boiler pressure will/should fall, this PRV should be set to 1.5 bar and only opened if the boiler pressure falls to ~ 1 bar cold.
Can you take a close up of the Wilo Fluid Control pump before closing anything.
1641993157735.png



This pump is switched off on the wall and hasn't been used for a long time from what I can see. I did try turning off the red lever yesterday and bleeding the radiator for awhile without any luck. Wanted to make sure I wasn't stopping flow to the cylinder too
 
Both those PRVs which are set to 4 bar may have one reducing the mains pressure for the cold water supply and the other may be reducing the mains pressure for the cold water supply to HW cylinder and maybe just flowing through the stopped (free wheeling) pump now.
You might see a braided hose somewhere on the supply to the boiler or system with isolation valves.

Even though you did shut that red lever valve maybe check out the indicated 15mm T off.

Edit. Or thy the other indicated one in ....rev1
 

Attachments

  • image_67174657.JPG
    image_67174657.JPG
    505.2 KB · Views: 9
  • image_67174657 rev1.JPG
    image_67174657 rev1.JPG
    508.6 KB · Views: 9
Both those PRVs which are set to 4 bar may have one reducing the mains pressure for the cold water supply and the other may be reducing the mains pressure for the cold water supply to HW cylinder and maybe just flowing through the stopped (free wheeling) pump now.
You might see a braided hose somewhere on the supply to the boiler or system with isolation valves.

Even though you did shut that red lever valve maybe check out the indicated 15mm T off.

Edit. Or thy the other indicated one in ....rev1

The pipe in your 2nd pic seems to go into the cylinder
image_67158017.JPG


Those pipes in my original post are the only ones going into the boiler. Can't find a braided hose anywhere
 
A bit unusual to have mains direct to a HW cylinder, except that you have a heat store?, where the boiler heats and circulates the water around the cylinder and the hot water is supplied via a coil in the cylinder, can you see what type of system you have got, it's strange but the top PRV has a marker needle on the pressure gauge which may be a clue to something?.
If the system is like I described then the boiler pressure will be the same as the (unvented) store pressure.
 
A bit unusual to have mains direct to a HW cylinder, except that you have a heat store?, where the boiler heats and circulates the water around the cylinder and the hot water is supplied via a coil in the cylinder, can you see what type of system you have got, it's strange but the top PRV has a marker needle on the pressure gauge which may be a clue to something?.
If the system is like I described then the boiler pressure will be the same as the (unvented) store pressure.
Really appreciate your help! I've just turned on the hot water which also does the radiators upstairs and these pipes are hot which lead into the cylinder:

Boiler:
 
Last edited:
Well, I can see that the bottom PG is now showing ~ 6 bar, it was 4 bar in your original photo, so something amiss there like a failed expansion vessel. Can you take a photo of the label on your cylinder also (sometime) a few "still" photos of all the connections on the cylinder.
 
Sorry Peter but really can't make much sense of that system, others on here may, I saw actually that both pressure gauges went to 6 bar with boiler on, if they fall back when boiler off or some hot water used then definitely points to a expansion vessel problem, although even at 4bar if connected to the boiler then the boiler PRV (safety valve) should be continuously passing as it should be a 3 bar PRV. If it is only passing at 6 bar but not at 4 bar then something seriously amiss IMO.
It looks as if the house system was originally pumped from the tank in your attic and converted to a mains only supplied system, do you recall any mods being made in your time there?.
There should also be a T&P PRV on the cylinder which opens at 90C or 7bar pressure, also a expansion valve on the cold water supply to the cylinder which opens at 6bar in the event of expansion vessel failure. If this cylinder is a store then safety devices may be different as not familar with them.

Some boilers (mainly combi I think) have a automatic top up system with the mains permanently connected, these are known to cause over pressure problems as well.
 
What happens if you turn the water mains off ?

Also please put the boiler case back on as it’s important
 
Yes just make sure boiler isn’t heating the system
 

Reply to Pressure too high in open vented system in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
139
Hi, My current hot water system needs to be replaced. Anyone got any suggestions or can recommend any plumbers around Derrimut area that won't rip me off? An office guy recommended me to apply for government rebates and get it installed through timetosave.com.au. How reliable is this...
Replies
6
Views
301
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
252
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock