Search the forum,

Discuss New Radiators Not Working in the Central Heating Forum area at PlumbersForums.net

Messages
5
In May I had my garage converted into a room & the builders plumber A, fitted a new radiator in there & moved the one in the hall

In June my plumber B, fitted a new gas boiler.

Now I've had the central heating on I've found the 2 new radiators don't heat up - all the other radiators in the house get red hot.

A is saying that B has left an airlock in the system - B is saying that A hasn't fitted the new rads correctly.
  • I have bled the new rads & there is no air in them
  • The pipe to the inlet valve of the hall rad gets hot but the rad doesn't
  • If I shut down all the old rads, the new rads get hot, although not as hot as the old ones
  • I've left the system running for 2 hours
  • After getting the new rads hot, if I open the old rads, the new ones go cold
  • The new rads are plumbed in 10mm pipe, all the old system is 15mm
Any suggestions what the problem is please
 
Last edited:
For a start guy who fitted boiler should have made sure all radiators worked before leaving job. As many pictures of install boiler ect as you've got please.
 
Open up the lockshield valves on the opposite end of each rad, maybe they haven't been balanced properly, open them right up and see if the rads get hot. If that works you'll need to balance them, I think there's a radiator balancing thread on here somewhere.
 
 
Sounds like not balanced correctly also how many rads do you have in the house ?
 
There are 9 rads inc the new one & replaced one.

I suspected a balancing issue - would the fact that the newly fitted rads being on 10mm pipework vs old rads on 15mm pipework cause that sort of problem?
 
Yep as 15mm will flow easier than 10 mm close all the lockshields shut and open the 15mm ones 1/4-1/2 of a turn the 10mm ones 1/2-3/4 of a turn if you get some that are slow / not heating up open it a bit more
 
In May I had my garage converted into a room & the builders plumber A, fitted a new radiator in there & moved the one in the hall

In June my plumber B, fitted a new gas boiler.

Now I've had the central heating on I've found the 2 new radiators don't heat up - all the other radiators in the house get red hot.

A is saying that B has left an airlock in the system - B is saying that A hasn't fitted the new rads correctly.
  • I have bled the new rads & there is no air in them
  • The pipe to the inlet valve of the hall rad gets hot but the rad doesn't
  • If I shut down all the old rads, the new rads get hot, although not as hot as the old ones
  • I've left the system running for 2 hours
  • After getting the new rads hot, if I open the old rads, the new ones go cold
  • The new rads are plumbed in 10mm pipe, all the old system is 15mm
Any suggestions what the problem is please
NO air in rads is not the same as air in the main circuit. New boilers have low pressure pumps so often between 1-1.5bar. Any air in the system is always going to be at atmospheric pressure i.e. 1 bar. So fighting 1bar with a system that is 1.5bar before losses is never going to happen. You only have 2 options (forget this whole balancing thing, that was in the old days before variable speed pumps) You have to remove air by hiking up the pressure (to the point before the relief valve kicks in) to 2.75 bar so you can fight the air lock or you need to do a full re-circulation i.e. push water through until it has been round ever rad and pipe bend/high point. And before I hear the siren call of "the joints will burst" consider this. If your pipework cannot handle 3 bar then the problem you have is minor compared to the cost of what you have to do to fix the underlying pipe problem.
 
NO air in rads is not the same as air in the main circuit. New boilers have low pressure pumps so often between 1-1.5bar. Any air in the system is always going to be at atmospheric pressure i.e. 1 bar. So fighting 1bar with a system that is 1.5bar before losses is never going to happen. You only have 2 options (forget this whole balancing thing, that was in the old days before variable speed pumps) You have to remove air by hiking up the pressure (to the point before the relief valve kicks in) to 2.75 bar so you can fight the air lock or you need to do a full re-circulation i.e. push water through until it has been round ever rad and pipe bend/high point. And before I hear the siren call of "the joints will burst" consider this. If your pipework cannot handle 3 bar then the problem you have is minor compared to the cost of what you have to do to fix the underlying pipe problem.
The new rads get hot when all, the other rads are closed off. Could there still be air in the main circuit in this instance?
 
No as they wouldn’t get hot try balancing them takes 10 minutes to do
 
May be worth checking the pump settings as well, if settable, as it may be set to some very low variable setting as suggested above.
 
The new rads get hot when all, the other rads are closed off. Could there still be air in the main circuit in this instance?
Now I'm not a qualified heating engineer with an NVQ but I do hold an MEng in electronics and I'm certified engineer through the engineering council so understand that what I say cannot possibly compete with an NVQ plumber but this is based on my personal experience in my home.
Large pipe run, air trapped. Cannot remove the air despite placing air vents in the pipework. My symptoms were radiators would work then they would not and they would alternate back and forth.
I had increased the pressure but the losses meant it could never reach the offending section of air. As I operate with low temperature heating, I decided to add an air vent in the offending section in the form of a large radiator. These videos of the commissioning of the large radiator might SOUND familiar to you. Video1 is radiator getting its first fill from the main 22mm primary pipe where I suspected the air lock was. Video 2 is opening the lockshield. Long story short, air gone, noise gone, system fine. 4 separate heating engineers had no idea what was happening because "they had never seen that before" LOL
In conversation with a retired plumber (some would say heating engineer) who specialised on schools and churches heating systems told me that it often took twice as long as the install job to remove the trapped air.
 

Attachments

  • 1.mp4
    6.6 MB
  • 2.mp4
    5.2 MB
Any air in the system is always going to be at atmospheric pressure i.e. 1 bar.
You are mistaken. It'll be at the same pressure as the water that surrounds it. In an unvented system, which is what I believe we are discussing, it'll be somewhere in the range 2–3bar (absolute). For for a vented system, the pressure is only 'atmospheric pressure i.e. 1 bar' at the top, i.e. the location of the free liquid surface in the expansion tank.
 
Last edited:
There has been no mention of the make/model of boiler or if the pump is even inside it.
If the boiler is less than 5 years old
You are mistaken. It'll be at the same pressure as the water that surrounds it. In an unvented system, which is what I believe we are discussing, it'll be somewhere in the range 2–3bar (absolute). For for a vented system, the pressure is only 'atmospheric pressure i.e. 1 bar' at the top, i.e. the location of the free liquid surface in the expansion tank.
so as you increase the water pressure you increase the air pressure making air impossible to remove from any system ever. Thanks for that. Just out of interest, how does that work with boyle's law? I've added a BBC bitezie for reference Volume and pressure in gases – the gas laws - Temperature and gas calculations - GCSE Physics (Single Science) Revision - BBC Bitesize - https://www.bbc.co.uk/bitesize/guides/zc4xsbk/revision/3
 
If the boiler is less than 5 years old

so as you increase the water pressure you increase the air pressure making air impossible to remove from any system ever. Thanks for that. Just out of interest, how does that work with boyle's law? I've added a BBC bitezie for reference

You don't seem to understand the difference between 'pressure', which does not affect the motion of bubbles, and 'pressure gradients', which do. In this context, Boyle's law tells you that as the pressure in the system water is increased the bubbles of trapped air shrink in volume.
 
Last edited:
You don't seem to understand the difference between 'pressure', which does not affect the motion of bubbles, and 'pressure gradients', which do. In this context, Boyle's law tells you that as the pressure in the system water is increased the bubbles of trapped air shrink in volume.
solubility of air in water...increase pressure..increase temperature...both increase solubility. So upping the pressure and temperature removes air locks as it dissolves the air in water. It's also known as Henry's law of solubility. You over think things bro
 
I really shouldn't rise to the bait of a straw man argument but anyway. . .

solubility of air in water...increase pressure..increase temperature...both increase solubility.
Wrong again. In the temperature range relevant to heating systems, the solubility of air in water decreases with increasing temperature.

So upping the pressure and temperature removes air locks as it dissolves the air in water.

If a system is air-locked at its normal operating temperature and pressure then the scope for increasing the pressure or reducing the temperature is too limited for this to be a viable way to fix the problem.
 
solubility of air in water...increase pressure..increase temperature...both increase solubility. So upping the pressure and temperature removes air locks as it dissolves the air in water. It's also known as Henry's law of solubility. You over think things bro

That must be the biggest load of crap I've heard on here.
 

Reply to New Radiators Not Working in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

The fittings below are for a mixer bar attached to a self contained shower. i.e not a wall. The attaching screws have snapped. I could get two new brackets, dismantle that existing one and start again or I could try and re attach via those screws, removing the broken ones from the plate and wall...
Replies
1
Views
216
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
7
Views
207
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
279
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
495
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
361
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock