Search the forum,

Discuss No hot water in the USA area at PlumbersForums.net

Messages
26
I have a 20 year old Megaflo system driven by a oil boiler, and never had this issue before. The water in the tank is cold, the system is switched to on, but nothing happens - the boiler isn't heating the water. I know the boiler is functioning otherwise, as is the pump because I can turn the central heating system on and the boiler fires and the pump pumps.
I'm assuming there's an electrical problem then: tank thermostat being the first suspect. The Honeywell 2way valve to the tank is closed, and when I move it manually to the open position, again, nothing happens (would I expect the boiler to fire and the pump to operate?)
This may be a coincidence but a hot water tap in a mainly unused shower room had been left slightly open for several days. The electric immersion has been used for hot water topping up due to guests being here so we didn't notice the issue until the immersion was switched off.
Is there something else I may have missed?
 
the valve for hot water opens and makes a micro switch to give power to the boiler and pump the problem is more than likely the synchrony motor in the valve, if you are good with electrics you can trace problem yourself either new motor or new valve head
 
the valve for hot water opens and makes a micro switch to give power to the boiler and pump the problem is more than likely the synchrony motor in the valve, if you are good with electrics you can trace problem yourself either new motor or new valve head
Thanks - I've had microswitch issues with other motorised valves in the past so maybe this is the problem.
 
Thanks - I've had microswitch issues with other motorised valves in the past so maybe this is the problem.
I think what GasMK1 means is the problem is more than likely the synchrony [synchronous] motor in the valve.

Personally I'd be inclined to test whether the system is attempting to power up the valve or not. I'm not really a fan of changing parts at random as a process of elimination: at that point you may as well finding a decent tradesman who can test before replacing. As you say, I'd suspect other things too, but agree GasMK1 is right in that the valve is generally the least reliable component.
 
I think what GasMK1 means is the problem is more than likely the synchrony [synchronous] motor in the valve.

Personally I'd be inclined to test whether the system is attempting to power up the valve or not. I'm not really a fan of changing parts at random as a process of elimination: at that point you may as well finding a decent tradesman who can test before replacing. As you say, I'd suspect other things too, but agree GasMK1 is right in that the valve is generally the least reliable component.
I did say if you are good with electrics and my starting point would always be checking wether power to valves, as they are indeed the weakest point.
 
I think what GasMK1 means is the problem is more than likely the synchrony [synchronous] motor in the valve.

Personally I'd be inclined to test whether the system is attempting to power up the valve or not. I'm not really a fan of changing parts at random as a process of elimination: at that point you may as well finding a decent tradesman who can test before replacing. As you say, I'd suspect other things too, but agree GasMK1 is right in that the valve is generally the least reliable component.
If the system is attempting to power up a faulty motorised valve, then if I manually move the valve to the on position, wouldn't you expect the system to work? If, on the other hand, the systems isn't calling for heat because the thermostat thinks it's hot enough, moving the valve to on wouldn't make any difference would it?
 
If the system is attempting to power up a faulty motorised valve, then if I manually move the valve to the on position, wouldn't you expect the system to work? If, on the other hand, the systems isn't calling for heat because the thermostat thinks it's hot enough, moving the valve to on wouldn't make any difference would it?
No as manually opening the valves doesn't close the microswitch which triggers the boiler and pump. The valve has to be powered up and the motor take it further to trigger the switch.

The only valves that trigger the microswitch in manually on are the DanFoss Valves.
 
No as manually opening the valves doesn't close the microswitch which triggers the boiler and pump. The valve has to be powered up and the motor take it further to trigger the switch.

The only valves that trigger the microswitch in manually on are the DanFoss Valves.
Ah - thanks - that's very useful. The central heating system valves are Danfoss and they fail every 2 - 3 years. The Honeywell has lasted 10 years or more.
 
No as manually opening the valves doesn't close the microswitch which triggers the boiler and pump. The valve has to be powered up and the motor take it further to trigger the switch.

The only valves that trigger the microswitch in manually on are the DanFoss Valves.
That's really helpful. I've removed the actuator, can operate the microswitch and it indeed triggers the system, so I'm assuming it's the synchron motor for now.
 
you need to check wether getting 240 to the motor if not then you need to check why not is there a call from timer is stat calling
 
Hi limit stat tripped out. Reset it.
Didn't know such a thing existed, and had a close look at the stat, as far as I could - it's quite inaccessible. There was a little red button which, when pressed, barely moved but made a click sound. Hey presto - the system is working! So huge thank you to everyone who has offered help and advice, especially EvilDrPorkChop who nailed it. For his efforts I am pleased to award him with this glittering trophy:
cup1.png
 
Didn't know such a thing existed, and had a close look at the stat, as far as I could - it's quite inaccessible. There was a little red button which, when pressed, barely moved but made a click sound. Hey presto - the system is working! So huge thank you to everyone who has offered help and advice, especially EvilDrPorkChop who nailed it. For his efforts I am pleased to award him with this glittering trophy:
View attachment 61406

The thing is if the limit stat triggered once, it may happen again. If it does it needs a qualified person to look into.
 
If it's around 20 years old, the estate I live on has them all. I have had a High Limit that's been faulty and kept triggering for no reason, i've had to replace it and was fine since but they're usually pretty sound. As SJB060685 has said though there maybe a reason for it why it's triggered.
 

Reply to No hot water in the USA area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
126
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
276
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
224
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
114
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock