My boiler is an Ideal Icos HE30 boiler. This supplies the central heating and a separate heat store - in other words a big cylinder - for domestic hot water.
It is not a combi boiler.
The boiler is 10 years old and it has been serviced by the original installer each year since installation. It has been reliable since installation.
The boiler is pressurised at 2bar.
Radiators fitted TVRs. All radiators heating OK. Radiators bled.
The CH system has a magnet debris filter.
No issues when the boiler is heating the DHW cylinder.
In the heating season each year I increase the boiler temperature control to near maximum.
This heating season the boiler has locked out a few times.
Fault code display alternates between L9 and H9 which relates to temperature monitoring thermistors.
Resets display without problem and then runs for another week or so before it locks out again.
I don't believe both thermistors have gone out of whack. So maybe a problem with water temperature?
At last week's annual service the boiler passed as good to go by the plumber. He confirmed that the pump was working correctly. The pump is a CPC CP63.
That said he was reluctant to get involved with resolving cause of the fault codes.
He said it could be one of many things and suggested I contact Ideal as it has special test equipment that could diagnosis the root cause rather than willy-nilly approach of swapping out of components.
I wonder given the extensive experience and knowledge of forum members their views, what the problem might be, and how it can be resolved in a cost effective manner.
 
It can be several issues as your engineer states, and perhaps it would be best to engage with Ideal for a fixed price repair. I think you could be right with the thermistors, and could be something as simple as the pump.
 
Codes you mention are over heat codes , ask your engineer to get his clamps out.
Also , boiler pressure from cold approx 1 bar not 2 bar and don't forget Icos’s were cheap low cost boilers , 10 years isnt bad for one ,however I have around 5 /6 on about 12 ish years old .
 
Thank you Townfanjon for your reply and advice.
A couple of more questions if I may.
Can you explain what his 'clamps' are and why they are relevant in finding the problem?
Is it a problem if the pressure is left at 2 bar.
Is there some sort of pressure sensor in the boiler controls that would be affected and contributing to the problem?
 
Can you explain what his 'clamps' are and why they are relevant in finding the problem?Is it a problem if the pressure is left at 2 bar.

Thermostat pipe clamps - checking temperatures.

2 bar not ideal (no boiler pun intended), not really much of an issue imo.
 
Ulsinus,

The use of temperature clamps are one tool for trying to diagnose the cause.

The boiler overheat trip is one of the last lines of defence ( before the prv) to prevent steam forming in pressure envelope. If the boiler is tripping on overheat, it should be properly diagnosed and repaired. Very often it is the result of a minor issue, but it can be a sign that there is something far more serious going.

Before you ask, you don’t want steam forming in the pressure envelope, if the prv fails you could get a very nasty surprise
 
Thanks Brambles.
Sadly that horse has bolted.
I mean to say the annual visit was last week and he didn't do it then.
So I'm reluctant to spend another £100.
[automerge]1605623550[/automerge]
The boiler overheat trip is one of the last lines of defence ( before the prv) to prevent steam forming in pressure envelope. ...
Thank you Brambles for highlighting this particular hazard.
Much appreciated.
 
Last edited:
Ok, but if a central heating system is tripping on over heat and it is still tripping on overheat after a service - it has not been serviced properly. By that I am not saying that the repair should be part of the service charge - but he / she should have made a recommendation and ideally price for further action to resolve the problem.
 
Last edited:
Hi,

I have resolved the issue.
I bought a set of clamps.
The source of the problem I believe was this:
'In the heating season ... I increase the boiler temperature control to near maximum.'
The boiler was simply running too hot.
I have set the flow temperature to approximately 65 degrees C with the aid of the clamps.
The house is toasty and the boiler hasn't locked out since.
Result.
Thank you all for your help, advice and insight.
 

Reply to Icos He30 combi boiler resolution L9/H9 fault codes in the USA area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
224
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
257
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
453
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
324
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock