I would like some opinions on this situation.
Vaillant Ecotec pro 28
Installed 2 years ago,
Commissioned Gas pressure reading 16.5mb at max rate.
1st annual service passed.(2018)
Just has second Service all combustion tests passed, and issued a Warning Advice notice of Immediately dangerous (ID) Reason Gas pressure on gas valve 14mbar, min requ 17mb.
Action: New 22mm gas pipe.
Vaillant Boiler installation and maintenance instructions says
Permissible gas flow pressure for operation with
G20 natural gas: 1.3 … 2.3 kPa (13.0 … 23.0 mbar)
Pressure at meter good, was checked by cadent with boiler on and all gas hobs on full.
No reply from original Gas safe installer.
Should I ask a for a second opinion on why it has classed a ID?
Boiler was switched off, but gas was not capped off.
Would it be safe to run boiler ? ( has been working fine, with no faults, good flame)
Question, Approx How much would running new pipe on outside property cost from gas meter to boiler. Metre at front if house, boiler at back of house 1st floor bedroom.
Vaillant Ecotec pro 28
Installed 2 years ago,
Commissioned Gas pressure reading 16.5mb at max rate.
1st annual service passed.(2018)
Just has second Service all combustion tests passed, and issued a Warning Advice notice of Immediately dangerous (ID) Reason Gas pressure on gas valve 14mbar, min requ 17mb.
Action: New 22mm gas pipe.
Vaillant Boiler installation and maintenance instructions says
Permissible gas flow pressure for operation with
G20 natural gas: 1.3 … 2.3 kPa (13.0 … 23.0 mbar)
Pressure at meter good, was checked by cadent with boiler on and all gas hobs on full.
No reply from original Gas safe installer.
Should I ask a for a second opinion on why it has classed a ID?
Boiler was switched off, but gas was not capped off.
Would it be safe to run boiler ? ( has been working fine, with no faults, good flame)
Question, Approx How much would running new pipe on outside property cost from gas meter to boiler. Metre at front if house, boiler at back of house 1st floor bedroom.