I would really appreciate your view on this underfloor heating set-up.


I’m experiencing what sounds like a knocking noise from the manifold/pipework (can’t tell which) for a few seconds whenever the underfloor heating zones are switched on, so am wondering if it’s an issue with a valve or something.



I’m also seeing that the temperature gauge on the return is always higher than on the supply side as shown on one of the photos (and all the flow meters have always been in the fully ‘red’ indication). I think this due to the fact that the flow and return seems to be the wrong way around ?


I would be very grateful if you could take a look and confirm if the pipework all looks to be in the correctly fitted locations.


I’ve attached a few photos of my manifold system – I’ve been trying to work out what each component does and how it works.


Would appreciate any advice (not looking to carry out the work myself, but at least know what to look at first).

Thanks

IMG_2952.JPG
 
Good afternoon,

it looks like a Polypipe manifold to me which has got the flow meters at bottom bar.
The control pack is not Polypipe, looks like Rifeng Inta Eco Ecomix.
What you need to do unscrew the manifold bars from the brackets and swap them so flow meters will be at the top of the manifold.
At the moment pump is trying to push the water through the return bar where the actuators are and they need few minutes to be fully open.
I've also done some research ref this mixing valve to ensure flow and return are connected properly and that seems to be fine (see image attached).

That should resolve all problems.

All the best,

Wojtek Zareba @ Uheat UFH

Rifeng-Inta-Eco-ECOMIX-15kW-Underfloor-Heating-Temperature-Control-Pump-Mixer-291623940173-11.jpg
 
Thank you very much for taking a look at this and posting a reply so promptly.

You're correct that it is an inta eco mixer but I couldn't see the arrow markings you've now shown too. The top rail is hotter than the bottom so that confirms the hot water is flowing through the pump upwards correctly, but I can see now that the rails is the wrong way round.

The only thing I don't know is what make the manifold is as there's no markings on it that I can see but all the the other fittings look like Watts.

Appreciate any other advice also.

IMG_2989.JPG


IMG_2979 2.JPG
 
Thank you very much for taking a look at this and posting a reply so promptly.

You're correct that it is an inta eco mixer but I couldn't see the arrow markings you've now shown too. The top rail is hotter than the bottom so that confirms the hot water is flowing through the pump upwards correctly, but I can see now that the rails is the wrong way round.

The only thing I don't know is what make the manifold is as there's no markings on it that I can see but all the the other fittings look like Watts.

Appreciate any other advice also.

View attachment 35360

View attachment 35361

I think is a Polypipe manifold. It doesn't make any difference to be honest, you can swap the bars around anyway.
Thanks,

Uheat – Wojtek
 
Thanks for clarifying.

One other question, once the bars are swapped around, how do set the flow rates to the correct level (are there any instructions anywhere ?) - how to determine what they should be also (based on length of piping laid ?).

I've had the system in for almost 3 years now, but as it's been off all summer, I haven't had to put up with any issues, but know that this needs to be corrected now. Is there any possibility of the pump or actuators having been damaged as a result of the bars having been installed the wrong way around.

Thanks again.
 
Thanks for clarifying.

One other question, once the bars are swapped around, how do set the flow rates to the correct level (are there any instructions anywhere ?) - how to determine what they should be also (based on length of piping laid ?).

I've had the system in for almost 3 years now, but as it's been off all summer, I haven't had to put up with any issues, but know that this needs to be corrected now. Is there any possibility of the pump or actuators having been damaged as a result of the bars having been installed the wrong way around.

Thanks again.
Good morning,
I don't think the actuators became damaged but you never know.
Pump - same again, difficult to judge.

Flow rates - they will depends on circuit lengths.

Many thanks,

Uheat – Wojtek
 
Thanks

I was testing the system again just now, and noted that the 'banging' noise starts a minute or so after the zone is activated - at this point, the pump is already pumping as it has a green light, and so it seems that the noise starts when the actuator is actually opening whereas I would have expected it to be almost immediate if it was due to a delayed activator as described above.

Could there be another issue for the banging also (water hammer).

Appreciate the advice again

Thanks
 
Thanks

I was testing the system again just now, and noted that the 'banging' noise starts a minute or so after the zone is activated - at this point, the pump is already pumping as it has a green light, and so it seems that the noise starts when the actuator is actually opening whereas I would have expected it to be almost immediate if it was due to a delayed activator as described above.

Could there be another issue for the banging also (water hammer).

Appreciate the advice again

Thanks
Hi
Was the banging noise issue resolved when you swapped the flow and return bars round? Or did it keep happening? We have had the banging noise issue and found our bars seemed to be the wrong way round. We have just swapped them and I am hoping I won't hear the banging noise again....
 

Reply to Flow and return the wrong way around in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
243
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
194
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
231
Hi all Noticed bad smell in my drain out side put my hand down and it unclogged it for now however I checked my sewer drain and after flushing my toilet a good few times nothing is going to the sewer so don't know is there a blockage or what way it works many thanks and advice would be grateful
Replies
3
Views
498
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock