Check oil hoses are done up tight and right way around or tiger wont prime.
Ive done it myself!
 
you could also try with a bucket filled with oil and using that as the tank if you like...just to see whether it's related to a supply issue
 
Went to the above boiler to do a service as requested but I stupidly forgot to test fire it before I pulled it apart.

Gave it a clean out, new nozzle and new oil lines.
Then when I fired it up it was stop start stop start then eventually locked out.
Checked the oil tank and there is plenty of oil and no contamination. (Brand new filter)

cant get any pump pressure. So changed the oil pump.
New oil pump fitted (although doesn't seem to be the exact same model even though part numbers are right as it's not got pressure and vacuum ports on the front.
Still the same.

Swapped the tiger loop (above burner) over quickly and still locking out. Just can't get any oil through it.
Cant check the pump pressure though as the test port is on the underside of the new oil pump.

Am I being really thick as it must be something really simple. Just every time I go there it's like 5-6 at night and dark and my brain is frazzled.

Cheers for any suggestions.


Any update on that ?
 
Not been able to get back as it's a charity and they arnt there most of the time. Just waiting on a time when our timetables cross.
 
Finally got back to this one. Fitted the correct oil pump. Changed a hose that was sucking in air and she is running like a goodun.
 
Status
Not open for further replies.

Reply to Worcester Danesmoor Wallhung in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi My oil boiler keeps locking out after running for 30/40 minutes! I then try to reset it but it won’t fire back up! I have to leave it for...
Replies
19
Views
854
I'm looking for some advice on a frustrating problem I'm having with my old Eurostar 50-60s oil boiler please? Although it's old, most parts...
Replies
3
Views
761
Any advice welcome as plumber stumped Had 36-46 grant vortex utility boiler 7 years no problem recently oil tank move and tigerloop install...
Replies
4
Views
619
I have a SIP space heater and fitted a new matching spec oil nozzle as part of a service on it. I wanted to check the pump pressure with the new...
Replies
2
Views
335
Hi there. I have Grant oil fired boiler which when cold, takes multiple times to fire up. It will run for say 20 or 30 seconds with hot exhaust...
Replies
1
Views
768
Back
Top