Discuss Use of microswitch on Honeywell 2-port valve for auxilliary pump in the Central Heating Forum area at PlumbersForums.net

Messages
10
My boiler struggled to circulate throughout my house so my heating engineer installed an auxilliary pump a few years ago. On a recent service he identified that the auxilliary pump was not working. He said that it was down to the motorised valve and he wants to charge £350 to replace it. He said that there was no power via the microswitch on the valve when it was open. The valve was new in Jan 2018 (replaced by same heating engineer when the auxilliary pump was installed).

I have two questions:
  • Is it intended that the microswitch be used to directly switch a load such as a pump? I see from spec on unvented components europe website that Auxiliary Switch Rating is 250VAC 4A so I assume this is OK (but wanted to check)
  • Is replacing the valve really necessary or should it be first attempted to just replace the Powerhead? If it is just replacing the PowerHead then £350 sounds really excessive - right?
 
No it’s not rated for a pump load should be used via a 6 amp relay

Yes does sound high
 

Reply to Use of microswitch on Honeywell 2-port valve for auxilliary pump in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
179
PSxxxxxx
P
My son has an apprenticeship interview for to become a plumber and heating engineer. The have said there will be a multiple choice exam for this for suitability. The thing is my son panics during tests/exams. Is there any book I can buy him to practice the multiple choice test for the exam? What...
Replies
3
Views
418
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
472
I want to reconnect some outbuildings to an existing water supply. The supply pipe is old 22mm MDPE and buried for a fair distance so not going to dig it up and replace it 😬. Question is can I use normal 22mm plumbing push-fit connectors to make the connection as finding 22mm MDPE fittings...
Replies
1
Views
268
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock