on31ll

Anybody know of a controller able to control 5 manifolds with 10 zones on each manifold


back story is its installed in a church 5 manifolds on the wall all fed off a domestic boiler. All manifolds fed in 22mm. The church left the heating on for 3 days solid and it moved up one degree !!!!!
 
That's alarm bells
Did you install it?
Does it have a low loss header?
How many kW is the boiler?

From the sound of it you want to pair the loops into large zones!!!
 
back story is its installed in a church 5 manifolds on the wall all fed off a domestic boiler. All manifolds fed in 22mm. The church left the heating on for 3 days solid and it moved up one degree !!!!!

I would be asking for the PI insurance details for the M&E consultant who designed it.
 
Well i want to link the zones out. No i didnt design or build that. Fed off a domestic 70kw boiler when. I go there ill take pictures its up there with bad installs.

No low loss header. Flow amd return straight into 5 manifolds
 
First things first that will never heat up....

Till the mixers reach temp their pumps will be pulling through the boiler!!!
5x a ups2......

That's going to exceed the max flow rate of the boiler massively and strip the heat too quickly
 
Sorry just a domestic 42kw. I was reading the post of the two 70kws.


Anyone suggest best ways to plumb this in. Im thinking two boilers. Low loss header. Need to sort pumping out though.
 
Get a firm in to do a independent heat calc and have them guarantee that.
Then compare to the underfloor spec and see if it's man enough, if not you'll need an auxiliary heat source for the warm up imho like the fanned myson rads.

your manifolds all want their flow and returns going to a manifold straight off the llh.

They can pull from there then and not the boiler, will give it half a chance to heat up!
 
I think that domestically the Honeywell evohome with 5 manifold kits could handle 50 zones although I'm assuming you have one or two stats per manifold ? . However that's gonna be pricy :)
 
In theory could i fit a zone valve to the flow on each of the 5 manifold and have each manifold as a zone. On a thermostat ?

Seems that would be alot easier. Really need to map out each one of these 50 zones
 