First I would check the setting of the manual by pass valve with the red handwheel, put a mark on the top of the handwheel at "12 oclock", then turn the hand wheel very slowly clockwise and carefully note the portion of a turn or the full turns required to close it fully, (should be ~ 3 to 4 full turns between fully open and fully closed) then return it initially to the same setting, you may find a 1/2 turn or so of play before the valve starts to reopen so allow for this, (of course if the valve has been left fully (unlikely) open then you will get 3 or 4 full turns to close it)
The main pump is running on full speed (3) which is 8M, I would change that immediately to speed 1 which is 6M and still more than adequate IMO, the 8M setting is probably the reason for the UFH flowrates doubling when UFH running alone. To change the speed, just press the setting button briefly a few times to highlight
I (solid green), that may still be too powerful at 6M but we'll see.
The manifold pump is running on minimum speed in fixed speed (CC) mode so leave that as is even though constant pressure (CP) mode is recommended for UFH.
THe UFH seems to be emitting a fair amount of heat, at T+15, CH+UFH on, a total flow of 5LPM with flow/return of 44C/28C gives a output of 5.59kw and at T+50, UFH on its own,, a total flow of 10LPM with flow/return of 44C/34C gives a output of 6.98kw.
You might run a few more tests after changing the pump speed and checking the bypass opening. Maybe just run the UFH only for 15/20 minutes or so to speed things up., you can then run on both once you post the UFH findings.