@Kurt Stone - thanks. I have an automatic bypass value fitted along with a gate value (photo attached with yellow line showing bypass valve). If I were to close the gate valve and then open it one turn, would that be similar to what you did?
Where is the photo of the above?.
Re your tests:
At T+15, with both CH&UFH on, the UFH shows flow/returns of 48C/27C with a combined flowrate of 5LPM, this is a UFH output of 7.33kw, at T+40, UFH only on, UFH flow/returns of 49C/34C, combined flowrate 10LPM = UFH output of 10.5kw, in both cases, dts of 21C & 15C seem way higher than normal of ~ 7C to 10C.
Also, at T+20 & T+25, CH only on, the UFH still shows a combined flow of 10LPM? can you check your labelling again?
The UPS2 8M pump at any "fixed speed" setting will pump at a head of 6M at even the lowest setting., might be able to suggest a more suitable setting even though there is no constant pressure mode on that pump.
THe ABV at any index setting will have a very high flowrate at speeds 2&3 (7M &M) and will cause rapid cycling and might even still pass at speed 1 (6M).
So,
Check the pump setting.
post a photo of the bypass with the manual valve & the ABV and its make and setting.
what is/was the boiler flow target temperature at the above tests?