currently pricing a job that involves gas mains running through communal corridors underneath the floor and branching off into apartments feeding the meters.
Now i know the regs regarding the pipe has to be welded/threaded steel OR in a fire rated duct and iv told the developer such but hes insisted on tracpipe, hes been advised elsewhere that tracpipe is the most cost effective and best way of this. Now my question is, is tracpipe counted as being exempt from the fire rated duct, i.e in the same bracket at the steel pipe. I know its sleeved stainles steel. I cant seem to find any info online. Any advice will be appreciated,

thanks in advance
 
Gas tite/ trac pipe is fine just need to be run in a sleeve if going through an unvented void / not the same property and fire collar it through any fire walls / floor by floor

They both are fire rated / hold certs

if you give me some time I will upload them
 
Sean,

I (we) have been caught out (quite rightly) with Flexigas pipe. On two runs the outer covering was slightly damaged ( abrasion where it had rubbed on the ground during installation). The certification for the pipe is that the outer covering is completely in tact and undamaged - to allow the outer plastic coating to act as a duct for a gas pressure of up to 2bar in the event of a leak. The Certification for Omegaflex - Tractpipe is the same. We had to replace two complex 30m runs ! - They could not be jointed.

Also bear in mind that all joints must be accessible and in a ventilated space - the “self ducted“ certification ends at the point the outer plastic covering is cut.

With the benefit of hindsight we sent two people to the Omegaflex training day - very well worth the time and cost. If nothing else, the tips and techniques given resulted in all subsequent joints (to date) being right first time and completed faster.

I am not advocating that Tractpipe is any better than other products in the market - but the installer needs to understand and know the vagaries of the product he / she is installing.

Apologies if this sounds tedious, but the mistakes we made cost our insurer nearly £5k
 
cheers Brambles, i wasnt aware of that with regards to the sleeving! Thanks for the heads up. Im going back to site tomorrow for a meeting. See what the other options will be.
[automerge]1588703904[/automerge]
Gas tite/ trac pipe is fine just need to be run in a sleeve if going through an unvented void / not the same property and fire collar it through any fire walls / floor by floor

They both are fire rated / hold certs

if you give me some time I will upload them

hi shaun,

so if i was to run a gas main at high level down a communal corridor in tracpipe it would definitely need to be houses in a duct? Or would it be ok? It wouldn't fall under the same classification as the steel pipe?And if it does require a duct does it need to be accessible? Im aware il need to vent it but will i need hatches wherever there is a fitting? The fittings are compression so im assuming they will. Im goin to site tomo to see all the options available
[automerge]1588704031[/automerge]
Brambles has answered that about the joints being accessible, i think i might suggest copper if we are going to use a duct anyway! Alot lot cheaper and probably easier all round. The developer was insistent but il have another look tomorrow
 
Last edited:
Where are the meters going normally do a single length to each flat (meters communal or external)
 
Sean,

Please don’t read my comments as a negative. My view is that coated corrugated stainless pipe is very good and better that a “ducted” pipe installation - but you need to detail on an itemised basis the specific routings / access points / all the fittings / required ducts and fire stops before you price the work - assuming it is lump sum.

As a guide, our pricing in Oxon to supply and install a 28mm Trac Pipe straight coupling is £58 - so your take off needs to be spot on.
 

Reply to Trac pipe, does it need a fire rated duct?? in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
231
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
110
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
322
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock