W

Wayne74

I have a Rehau underfloor heating system on the ground floor only of my house. Every so often, the manifold makes a knocking/thumping noise. When I look at the flow meters I can see the one that's making the noise and the little ball in the flow meter is bouncing up and down (so the water level is bouncing up and down, obviously). Could this be air in the system? It only does it when there is demand on that particular loop (the hall, so there's often demand as the temp changes due to the front door being opened). If I turn the pump speed down it simply changes the tempo of the thumping! Any ideas? The flow meters are beginning to look opaque so I guess the system needs cleaning out anyway, but the thumping has occurred on and off since the system was installed (now 5 years old).
 
Sounds like (boom-boom) you need to replace the TRV head for that particular loop. I've had it happen briefly when the head gets to a certain position while closing down (they can take a minute or two), but not constantly. Have you also tried tweeking the flow limiter &/or the flow/return blending valve?
 
Oh, and I wouldn't worry too much about a bit of visible discolouration in the flow limiter glass. Though if you've rads upstairs, have you got a magnet/filter on the primary return?
 
Just a thought: used to have occasional thumps on rad TRVs which were due to flow through valve being backwards! Have you checked the valve body to see if it's right way round for flow?
 
Hi Wayne,

does it just happen to one flow meter?
I've had a customer week ago with exactly the same symptoms at Uponor manifold.
He replaced the flow meters and the noise is gone.

Thanks
 
Hi Wayne,

does it just happen to one flow meter?
I've had a customer week ago with exactly the same symptoms at Uponor manifold.
He replaced the flow meters and the noise is gone.

Thanks
 
Status
Not open for further replies.

Reply to Thumping manifold, bouncing flow meter in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
316
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
117
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
141
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
119
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
241
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock