Defect ID:
Severity
Attributable To
I detected a gas escape when carrying out a gas tightness test of the NG
meter and gas installation pipework up to and including 28 mm diameter with
appliances connected for gas tightness in accordance with the Institution of
Gas Engineers and Managers Standard IGEM/UP/1B Edition 3.Tightness
testing and direct purging of small Liquefied Petroleum Gas/Air, Natural Gas
and Liquefied Petroleum Gas installations. The gas escape rate was not within
the accepted tolerances of IGEM/UP/1B Edition 3.
1
Unknown
NCS
Defect ID:
Severity
Attributable To
The adhoc cupboard that contains the gas meter requires alteration. The
cupboard door snags on the work bench in front of it making access to the gas
emergency control valve difficult.
4
Unknown
NCS
Defect ID:
Severity
Attributable To
I identified that the gas installation pipework within the catering area was not
fitted with a manual emergency isolation valve in the pipework to isolate the
gas supply in an emergency situation. British Standard 6173:2009
Specification for installation and maintenance of gas-fired catering appliances
for use in all types of catering establishments (2nd and 3rd family gases)
requires that a manually-operable valve shall be fitted in the gas supply to
every catering area to enable isolation of the supply in an emergency. Either
this valve shall be located outside the catering area or near an exit, and be in a
readily accessible position, or an automatic electric valve system shall be fitted.
In the latter case, an emergency stop button or control shall be located to
enable operation in an emergency. The control shall either be shielded or
located in a position where shielding is not required. A manually operable valve
can be fitted outside the catering area if it is totally impracticable to install this
in the catering area.
5
Unknown
NCS
Defect ID:
Severity
Attributable To
I identified that the gas installation pipework within the catering area was not
clearly identified. British Standard 6173:2009 Specification for installation and
maintenance of gas-fired catering appliances for use in all types of catering
establishments (2nd and 3rd family gases) requires that pipework shall be
clearly identified as carrying a fuel gas by painting the pipework yellow ochre
(to BS 4800 08 C 35) or primrose yellow (to BS 4800 10 E 53), or, alternatively,
by applying a Gas marker tape at suitable intervals along the pipework.
6
Unknown
NCS
Defect ID:
Severity
Attributable To
I identified that the gas installation pipework was not installed with a minimum
clearance of 25 mm from a surface. British Standard 6173:2009 Specification
for installation and maintenance of gas-fired catering appliances for use in all
types of catering establishments (2nd and 3rd family gases) requires that
pipework shall be installed with a minimum of 25 mm between the pipework
and an adjacent surface (such as a wall) to enable the pipework and the
surface behind it to be cleaned.
7
Unknown
376796/2970276
Page 12 of 17
NCS
Defect ID:
Severity
Attributable To
I identified that the gas installation pipework within the catering establishment
was not sleeved correctly. British Standard 6173:2009 Specification for
installation and maintenance of gas-fired catering appliances for use in all
types of catering establishments (2nd and 3rd family gases) requires that
where pipework passes through a sleeve to enter the catering area, the sleeve
shall be protrude no less than 25 mm from the finished surface of the wall or
floor where water or chemical cleaning materials may be used. Sleeves shall
be sealed with a flexible sealant at the kitchen side to avoid corrosive cleaning
substances building up inside the sleeve.
8
Unknown
NCS
Defect ID:
Severity
Attributable To
I identified that the gas pipework throughout the property was not sleeved.
IGEM/UP/2 Edition 2 (with Amendments August 2008) Communication 1729
Installation Pipework on Industrial and Commercial Premises states that where
pipework is installed so as to pass through walls or is installed to pass through
any floor of solid construction the pipework shall be enclosed in a sleeve and
the pipework and sleeve shall be so constructed and installed so as to prevent
gas passing along the space between the pipe and the sleeve (for example by
sealing one end) and so as to allow normal movement of the pipe. The
pipework was showing no signs of distress.
9
Unknown
NCS
Defect ID:
Severity
Attributable To
It was identified that there was no quarter turn manual isolation valve fitted in
the gas installation pipework supplying the catering appliances. British
Standard 6173:2009 Specification for installation and maintenance of gas fired
catering appliances for use in all types of catering establishments (2nd and 3rd
family gases) requires that in addition to the valves required by IGEM/UP/2, a
manual isolation valve shall be included in the pipework to enable each
individual appliance to be isolated for servicing, cleaning, etc.
10
Unknown
AR
Defect ID:
Severity
Attributable To
The visible gas pipework totalled more than 25m in length and supplied 7
catering appliances within the two catering/kitchen areas and possible duty for
an appliance(s) in the flat above. The pipework was a mixture of 22mm and
15mm copper tubing. In one instance 22mm pipe was reduced down to 15mm
and then back up to 22mm. A supply pipe to a possible multipoint water heater
in the flat was in 15mm tube.
13
Unknown
AR
Defect ID:
Severity
Attributable To
The gas meter supplied 7 catering appliances within the two catering/kitchen
areas and possible duty for an appliance(s) in the flat above. Further
investigation will be required as to the suitability of the gas meter.
14
Unknown
NCS
Defect ID:
Severity
Attributable To
I identified that the gas installation pipework was spaced less than 150 mm
from an electricity meter and/or consumer units and not separated by electrical
insulating material. This was not in accordance with British Standard 6891:
2005 +A2:2008 Installation of low pressure gas pipework of up to 35mm (R1¼)
in domestic premises (2nd family gas) – Specification. British Standard 6891:
2005 +A2:2008 requires that where gas installation pipes are not separated by
electrical insulating material, they shall be spaced at least 150 mm away from
electricity meters and associated excess current controls, electrical switches or
sockets, distribution boards or consumer units.
2
Non Gas Work
376796/2970276
Page 13 of 17
NCS
Defect ID:
Severity
Attributable To
I identified that the gas installation pipework was spaced less than 25 mm
from, an electricity supply/distribution cable and not separated by electrical
insulating material. This was not in accordance with British Standard 6891:
2005 +A2:2008 Installation of low pressure gas pipework of up to 35mm (R1¼)
in domestic premises (2nd family gas) – Specification. British Standard 6891:
2005 +A2:2008 requires that where installation pipes are not separated by
electrical insulating material, they shall be spaced at least 25mm away from
electricity supply and distribution cables.
3
Non Gas Work
APPLIANCE 1. Appliance 1. / Archway - Kebab Grill
NCS
Defect ID:
Severity
Attributable To
I identified that the flexible connection fitted to the appliance was not installed
correctly. British Standard 6173:2009 Specification for installation and
maintenance of gas fired catering appliances for use in all types of catering
establishments (2nd and 3rd family gases) requires that flexible connections
shall be in accordance with BS 669-2 and be installed in accordance with
manufacturers installation instructions. To prevent bending or stretching
damage to the connection, a smooth U shaped curve of the flexible connection
shall be achieved in any appliance position during withdrawal for cleaning.
11
Unknown
APPLIANCE 2. Appliance 2 / Archway - Kebab Grill
NCS
Defect ID:
Severity
Attributable To
I identified that the flexible connection fitted to the appliance was not installed
correctly. British Standard 6173:2009 Specification for installation and
maintenance of gas fired catering appliances for use in all types of catering
establishments (2nd and 3rd family gases) requires that flexible connections
shall be in accordance with BS 669-2 and be installed in accordance with
manufacturers installation instructions. To prevent bending or stretching
damage to the connection, a smooth U shaped curve of the flexible connection
shall be achieved in any appliance position during withdrawal for cleaning.
 
APPLIANCE 3. Appliance 3. / Unknown / Griddle, possibly ad hoc appliance. No makers mark visible.
AR
Defect ID:
Severity
Attributable To
Severely twisted flexible hose, under stress. I identified that the flexible
connection fitted to the appliance was not installed correctly. British Standard
6173:2009 Specification for installation and maintenance of gas fired catering
appliances for use in all types of catering establishments (2nd and 3rd family
gases) requires that flexible connections shall be in accordance with BS 669-2
and be installed in accordance with manufacturers installation instructions. To
prevent bending or stretching damage to the connection, a smooth U shaped
curve of the flexible connection shall be achieved in any appliance position
during withdrawal for cleaning.
15
Unknown
NCS
Defect ID:
Severity
Attributable To
I identified that that no restraining device has been fitted to the appliance.
British Standard 6173:2009 Specification for installation and maintenance of
gas fired catering appliances for use in all types of catering establishments
(2nd and 3rd family gases) requires that when a moveable appliance is
connected with a flexible connection a restraining device conforming to BS
669-2 is fitted. The restraining hardware shall be fixed to the building structure
and the appliance frame.
16
Unknown
APPLIANCE 4. Appliance 4 / Pitco Deep Fat Fryer
376796/2970276
Page 14 of 17
NCS
Defect ID:
Severity
Attributable To
I identified that the flexible connection fitted to the appliance was not installed
correctly. British Standard 6173:2009 Specification for installation and
maintenance of gas fired catering appliances for use in all types of catering
establishments (2nd and 3rd family gases) requires that flexible connections
shall be in accordance with BS 669-2 and be installed in accordance with
manufacturers installation instructions. To prevent bending or stretching
damage to the connection, a smooth U shaped curve of the flexible connection
shall be achieved in any appliance position during withdrawal for cleaning.
17
Unknown
NCS
Defect ID:
Severity
Attributable To
I identified that that no restraining device has been fitted to the appliance.
British Standard 6173:2009 Specification for installation and maintenance of
gas fired catering appliances for use in all types of catering establishments
(2nd and 3rd family gases) requires that when a moveable appliance is
connected with a flexible connection a restraining device conforming to BS
669-2 is fitted. The restraining hardware shall be fixed to the building structure
and the appliance frame.
18
Unknown
APPLIANCE 5. Appliance 5. / Shaan Tandoori
NCS
Defect ID:
Severity
Attributable To
I identified that the flexible connection fitted to the appliance was not installed
correctly. British Standard 6173:2009 Specification for installation and
maintenance of gas fired catering appliances for use in all types of catering
establishments (2nd and 3rd family gases) requires that flexible connections
shall be in accordance with BS 669-2 and be installed in accordance with
manufacturers installation instructions. To prevent bending or stretching
damage to the connection, a smooth U shaped curve of the flexible conn
 
APPLIANCE 6. Appliance 6. / Henny Penny / GA 010 IF
NCS
Defect ID:
Severity
Attributable To
Incorrect flexible hose used BS 699-1. British Standard 6173:2009
Specification for installation and maintenance of gas fired catering appliances
for use in all types of catering establishments (2nd and 3rd family gases)
requires that flexible connections shall be in accordance with BS 669-2 and be
installed in accordance with manufacturers installation instructions.
20
Unknown
NCS
Defect ID:
Severity
Attributable To
I identified that that no restraining device has been fitted to the appliance.
British Standard 6173:2009 Specification for installation and maintenance of
gas fired catering appliances for use in all types of catering establishments
(2nd and 3rd family gases) requires that when a moveable appliance is
connected with a flexible connection a restraining device conforming to BS
669-2 is fitted. The restraining hardware shall be fixed to the building structure
and the appliance frame.
21
Unknown
APPLIANCE 7. Appliance 7. / 6 Burner hotplate
376796/2970276
Page 15 of 17
NCS
Defect ID:
Severity
Attributable To
I identified that the flexible connection fitted to the appliance was not installed
correctly. British Standard 6173:2009 Specification for installation and
maintenance of gas fired catering appliances for use in all types of catering
establishments (2nd and 3rd family gases) requires that flexible connections
shall be in accordance with BS 669-2 and be installed in accordance with
manufacturers installation instructions. To prevent bending or stretching
damage to the connection, a smooth U shaped curve of the flexible connection
shall be achieved in any appliance position during withdrawal for cleaning.
22
Unknown
NCS
Defect ID:
Severity
Attributable To
I identified that that no restraining device has been fitted to the appliance.
British Standard 6173:2009 Specification for installation and maintenance of
gas fired catering appliances for use in all types of catering establishments
(2nd and 3rd family gases) requires that when a moveable appliance is
connected with a flexible connection a restraining device conforming to BS
669-2 is fitted. The restraining hardware shall be fixed to the building structure
and the appliance frame.
23
Unknown
376796
 
We recently visited your property to do an inspection on the gas work carried out by Unknown .. You can read the findings
from this inspection in the Unregistered Investigation Report overleaf.
Unregistered gas work
The work recently undertaken at your property has not been carried out by a Gas Safe registered business. By law, only
Gas Safe registered engineers can carry out gas work. The Gas Safety (Installation and Use) Regulations 1998 make
it a legal requirement that only suitably competent Gas Safe registered engineers are permitted to install, commission,
service or repair gas pipe work or appliances (e.g. boilers, water heaters, fires, cookers, hobs etc). A person convicted of
carrying out gas work when not registered with Gas Safe Register could face:
• a fine of up to £20,000 and up to six months imprisonment in a Magistrates’ Court (or Scottish equivalent), or;
• an unlimited fine and up to two years imprisonment on indictment in the Crown Court.
For multiple breaches, the penalties may be significantly higher.
Unsafe gas work
As the person responsible for your property, you should not use a gas appliance or allow someone else to use it if you
know or suspect that it could be dangerous. This is a requirement of Regulation 34 of The Gas Safety (Installation and
Use) Regulations. If checks and tests have identified gas safety defects, they are in the enclosed Defect Report section
of the Unregistered Investigation Report. Where gas safety checks and tests have not found unsafe defects, with your
permission the gas installation or appliance may have been left working. You will have received an Unregistered Gas
Work Advice Notice form. In the interests of safety, as part of our inspection we may have issued you with a Warning
Advice Notice. You could be putting your family, friends or other occupants of the property at risk if you use an appliance
or gas fitting classified as unsafe. It could cause a gas leak, fire, explosion or carbon monoxide poisoning.
Contacts
To fix the unsafe gas work you will need to employ a Gas Safe registered engineer . You can find a Gas Safe registered
business in your local area by phoning 0800 408 5500, or go to Gas Safe Register | Ensure your gas engineer is registered.. If you require any further
assistance please contact Customer Services on 0800 408 5500. Please ask for the Investigations Team quoting
Complaint ID 42795 which will help us to deal with your query more quickly. A copy of the enclosed Unregistered
Investigation Report has also been sent to the local office of the Health and Safety Executive for consideration .
Yours faithfully,
Nick Deakin
Regional Investigations Officer
Gas Safe Register®
 
On the 31 March 2014 I went XXXXXXXX as a complaint had been
received by Gas Safe Register. The complaint has been allocated a reference number of XXXX.
At the above address I met XXXXXX(EHO's, East Staffordshire Borough Council) and XXXX
(Staffordshire Fire and Rescue), also XXXX Heating and Plumbing a Gas Safe Registered engineer
who had worked at the property in December 2013. A gas escape had been identified at the property and the gas supply
disconnected by the gas emergency service provider. *** the cause of the gas escape and
repaired it and restablished the gas supply.XXXXX does not have the relevant ACS competencies to work on
commercial catering installations.
During the inspection as a result of a significant gas escape being identified soon after arrival at the property a visual only
inspection was then carried out.
While carrying out the inspection numerous issues were identified and are listed within the defect section of the report, as a
result of these defects the installation was classed as Immediately Dangerous in accordance with the Gas Industry Unsafe
Situations Procedure (GIUSP).
The commercial kitchen areas located at the property had mechanical extract systems which required natural ventilation.
The extract canopies were not fully checked during the inspection; therefore the responsible person(s) for the property are
advised to have the extract systems, and make up air provision checked/inspected by a suitably qualified person due to the
following reasons;
• Excessive ambient air temperature in the front catering/restaurant area,
• Appliances not suitably positioned under the canopy in the rear catering area
• No visible make-up air provision
• No evidence was available on site to confirm safe levels of CO² within the catering area.
31/03/2014
Unaccompanied
376796/2970276
Page 2 of 17
• No appliance safety check
 
Is that someone using your gassafe number?

or where you the one called out for a gas leak and just found all the rubbish left behind?

nice to see gas safe actually doing something though :)
 
No they've called us in to rectify it all and the more I read it the more I want to cry , just not got the time ll
 
Sound like fun day. Expect it's spotless and easy access too then?

Probs not want to pay and probably won't pay
 
Pretty much what I find at very one of these establishments, worst one was no interlock or vents or make up air, I swear you could not breath
 
Status
Not open for further replies.

Reply to someones getting there legs slapped in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
549
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the...
Replies
5
Views
319
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16...
Replies
0
Views
235
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock