Hi all,

Small radiator upstairs is not working.

When the heating system powers up all the radiators get hot expect one. When I bleed the radiator, hot water flows through into the radiator and out of the bleed valve.

I have swapped the thermostat valve with another radiator but it hasn’t worked. I think the pipe is blocked beyond the thermostat valve???

Trouble shooting I have done so far:
Valves replaced and cleaned.
Radiator taken off wall and flushed- No sludge present.
Radiator gets hot when bleed valve open so ‘in’ pipe isn’t blocked.

Heating system 5 years old and has no thermostat issues.
 
Hi all,

Small radiator upstairs is not working.

When the heating system powers up all the radiators get hot expect one. When I bleed the radiator, hot water flows through into the radiator and out of the bleed valve.

I have swapped the thermostat valve with another radiator but it hasn’t worked. I think the pipe is blocked beyond the thermostat valve???

Trouble shooting I have done so far:
Valves replaced and cleaned.
Radiator taken off wall and flushed- No sludge present.
Radiator gets hot when bleed valve open so ‘in’ pipe isn’t blocked.

Heating system 5 years old and has no thermostat issues.
Try turning all radiators off except the one which doesn’t work and see if it heats up.
 
If the TRV is on the return side, as it sounds from your original post, I'd check whether or not your TRVs are bi directional, if they aren't it should be on the flow side.

e2a if they're bi directional they'll usually have 2 arrows, if there's just one arrow its not bi directional.
 
bi-directional-honeywell-trv.jpg


That's the arrows on a bi directional, if there's only an arrow pointing towards the rad is uni directional (and should be on flow side). If there are no arrows at all, I'd swap it over onto the flow side and see how it goes.

Sounds to me like its either that or you've got a problem in your return pipe, considering you've got 10mm plastic it could well be a blockage.
 
I have the same / similar problem. The radiator in my study does not heat up, all others (13 out of 14) are fine. Steps taken so far: Bled system. Replaced lock shield valve. Replaced TRV body. With lock shield closed and TRV open, warmish water flows from the air vent. With lock shield open and TRV closed, similar result. With both valves open the flow from the vent increases significantly, but with the vent closed there does not seem to be any flow across the radiator. Gut instinct (and the flows mentioned above) leads me to suspect both flow and return are pressurised equally, so no differential pressure and thus no flow. Is this a possibility? If so, how could this happen and how do I resolve?
System is 16 years old, plastic 10mm piping. TRV bodies are Honeywell bi-directional. TRV heads are new Honeywell Evohome 92HR UK. All help appreciated.
 
Last edited:
Thanks Simon, but I don't think this could be the problem (but happy to be proven wrong!).
To elaborate, with all radiators closed off except this one and a towel rail (that is acting as a by-pass) I am only seeing minimal heat (barely warm) at this radiator. I have removed both the TRV and lockshield valves and visually checked they are both fully open, TRV body spindle free to move and TRV head removed so nothing obstructing the operation . I'm beginning to suspect either the radiator or one of the 10mm pipes is clogged up, so I will flush the radiator through in the next day or two. I'll also try closing off the towel rail too, so applying maximum pressure to the problem radiator (just wary of damaging the boiler by disabling the bypass with all other radiators closed). Any thoughts ?
 
Close off the towel rail as well. Shouldn't cause an issue with the boiler.

Can also disconnect flow and return to radiator and let it blast into a bucket.
 
With lock shield closed and TRV open, warmish water flows from the air vent. With lock shield open and TRV closed, similar result. With both valves open the flow from the vent increases significantly, but with the vent closed there does not seem to be any flow across the radiator. Gut instinct (and the flows mentioned above) leads me to suspect both flow and return are pressurised equally, so no differential pressure and thus no flow.
I assume the tests were done with the boiler not working so the pump was not running. In which case the test results are as expected. There will be very little difference in the pressure either side of a radiator when the system is not working. It's ony when the pump is running that you get any significant difference
 
I assume the tests were done with the boiler not working so the pump was not running. In which case the test results are as expected. There will be very little difference in the pressure either side of a radiator when the system is not working. It's ony when the pump is running that you get any significant difference
Actually, it was with the pump running. Looks likely that I have a blockage in the pipes or radiator. I will remove the radiator tomorrow and check the flow into a bucket as suggested by Simon. I will also take the opportunity to flush though the radiator. I’m hoping I’ll resolve or at least diagnose the issue tomorrow. Thanks.
 
Problem found... the pipe work in the wall has a kink in it. When I take the rad off the wall and straighten the pipes up, it works perfectly!

Thank you to everyone that has helped. Really Appreciated. I am glad I didn't go with British Gas's advice of a Power Flush-£700!!!
British Gas what a sorry outfit they are now populated by sales orientated numpties no wonder Centrica are trying to sell the outfit off but no one wants it Centralheatking
 

Reply to Small radiator not working in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
172
PSxxxxxx
P
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
7
Views
190
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
137
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
337
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
464
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock