Louise,
With respect to COP, with an ASHP running with an inverter, you really need an ultrasonic energy (heat) measurement meter fitting to the flow as close as possible to the pump. That will give you net output on an hourly / weekly / monthly et al. For gross input measure the electrical power consumption into the unit. Thereafter (over time) you will get reasonably accurate COP calculation. The cost of the equipment to install is around £300.
Measuring flow temperature does not give you anywhere near a credible COP with an inverter driven ASHP. That method is ok with fixed speed pumps on continuous running heating a swimming pool or a large UFH system.
In an earlier post, I think you cited a flow temperature of 65 degrees C - if that is true it needs to be reduced to an absolute max of 58 degrees C - beyond the issue of it delivering a very low COP you are at risk of damaging to coverings et al to your UFH - unless it has been set up with adequate provision to blend the flow down to around 45 degrees C.
I suspect that 65 degrees would also be outside the operating envelope for any Nibe warranty you may have.
With respect to COP, with an ASHP running with an inverter, you really need an ultrasonic energy (heat) measurement meter fitting to the flow as close as possible to the pump. That will give you net output on an hourly / weekly / monthly et al. For gross input measure the electrical power consumption into the unit. Thereafter (over time) you will get reasonably accurate COP calculation. The cost of the equipment to install is around £300.
Measuring flow temperature does not give you anywhere near a credible COP with an inverter driven ASHP. That method is ok with fixed speed pumps on continuous running heating a swimming pool or a large UFH system.
In an earlier post, I think you cited a flow temperature of 65 degrees C - if that is true it needs to be reduced to an absolute max of 58 degrees C - beyond the issue of it delivering a very low COP you are at risk of damaging to coverings et al to your UFH - unless it has been set up with adequate provision to blend the flow down to around 45 degrees C.
I suspect that 65 degrees would also be outside the operating envelope for any Nibe warranty you may have.