B

Bibbs

Evening Gas Dudes.

I require I little tech help with a ravenheat csi 85, combi with the dual pass heat exchanger and one thermistor.

So I went to the job, boiler knocking off when using the shower, sometimes going to lock out.

I cleared (on first visit) then replaced the thermistor on 2nd visit, also replaced the gas valve on 2nd.

I diagnosed the gas valve as it wouldn't module on the dhw stat, although I couldn't get my gauge on P2 as it was seized up, I checked for DC volts on modi reg and this was about 13 and did drop when I turned the DHW stat down.

From the flame pic I could see it wasn't dropped the pressure and the flame didn't move at all when I pulled one of the leads off the modi reg.

Ok so today I fitted the gas valve and it now modules on the DHW stat BUT not if I back the tap off, the water is plenty hot enough so I don't think the D/P heat ex is blocked.

However, and I don't think this has caused a problem but worth mentioning, but I got 240 volts of the modi reg lead because there was an out clock and fuse spur which had been turned on in between my first and 2nd visit by the electricians who had done a rewire on the house. Once I figured out where the 240 was coming from I isolated the fuse spur and proceeded to fit and test the new gas valve and got moduleation as described above. I'm thinking the potentiometer may be at fault but thought I'd ask on here before I buy one.

(i also got 240 yesterday off a pump wired from consumers unit, how many days on the bonce do I need to get 240 belts before I get super powers?)
 
Not going to get an answer in the open forum.
Need to up your post to ten and contact one of the mods
 
Last edited:
Status
Not open for further replies.

Reply to Ravenheat CSi 85 in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
7
Views
186
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
119
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
452
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
128
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
245
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock