4
i have a hot water tank and gas boiler and for the last 4 months my boiler turns on when I use some of my hot water like it’s reheating the bit I just used.

This wouldn’t normally be an issue but my entire heating system is set to off for the summer.

How or why is my boiler reheating the hot water when everything is turn off.
 
If you do have a 3 port, then this valve sits in the hot water position when powered off, so that would lead to me think you have a fault with your programmer. It may be set to off but could still be sending power to the cylinder thermostat. When you use your hot water, the temp in the tank drops causing the stat to call for heat which will then bring your boiler on. This is only one possible cause though so I'd recommend you get a plumber out to check the system and electrics over.
 
I did wonder if it was the programmer but then I also wondered whether it was the actuator that had broken and was stuck. You’re right the a plumber coming is the best option I did want to change to a nest setup soon anyhow so maybe I’ll do it sooner than I planned
Thxs for your help
 

Reply to Hot water turning on issue in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
117
Hi bit of a weird issue, I installed a grohe bathroom tap successfully 2 months ago bought from screwfix. Last week the right hand hot tap makes a squeak noise as I turn it on or off, left tap is 100% perfect and noiseless. This grohe tap is like one unit, so no screw notch or way I can remove...
Replies
1
Views
83
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
252
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
319
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
222
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock