Honeywell 4043H1056 just installed to replace ESi which was leaking. HW is banging on closing whereas ESi didn't!! Both are power opening, spring closing. HW was installed in the same direction in the return pipework. Arrow points towards the tank. Is that correct? Need another to replace my 2nd ESi but hesitating to get another HW despite their good reputation. Any thoughts would be very welcome.
 

ShaunCorbs

Staff member
S. Mod
Plumber
Gas Engineer
Is there an auto bypass fitted as if there isn’t there’s your problem
 

heliotrope

Plumber
Gas Engineer
The arrow on the zone valve would be pointing to the cylinder if on the flow.

You say that the valve is on the return from the cylinder then the arrow should
be pointing away.

It would seem you have mounted the valve the wrong way round.
 
Bulk Workwear - Workmans Clothing and Protective Gear
This official sponsor may provide discounts for members

RoryD

Plumber
Gas Engineer
Honeywell 4043H1056 just installed to replace ESi which was leaking. HW is banging on closing whereas ESi didn't!! Both are power opening, spring closing. HW was installed in the same direction in the return pipework. Arrow points towards the tank. Is that correct? Need another to replace my 2nd ESi but hesitating to get another HW despite their good reputation. Any thoughts would be very welcome.
The ball swells up in them and seating is an issue. You can get a Honeywell ball valve kit to replace the plate / ball. Or you could just replace the valve. I'm imagining it sounds like a drum roll on a Bongo drum?
 

Gasmk1

Gas Engineer
Advent Win
The ball swells up in them and seating is an issue. You can get a Honeywell ball valve kit to replace the plate / ball. Or you could just replace the valve. I'm imagining it sounds like a drum roll on a Bongo drum?
op says its a new one
 
I think we need to check for simple causes like correct orientation first though mate.
OP here again! Looks like it is the wrong way round after all. Reason being that my second tank is piped the opposite way to the first one and when the first one leaked the replacement valve was installed to be like the other!! So arrow should indeed not be pointing to the tank when it is in the return. Second draindown and ZV replacement next week will be the final proof!
Thanks to all who replied
 

Reply to Honeywell Zone valve banging on closing in the Central Heating Forum area at PlumbersForums.net. Plumbing questions, answers, tips and tricks.

Plumbase Perks - Special offers for forum members
This official sponsor may provide discounts for members
Plumbing Advice - Find Plumbers Jobs
Wetroom Store - PlumbersForums.net Sponsor
Corgi Direct - Plumbers Forums Sponsor
uHeat Forum Sponsor - PlumbersForums.net
Bulk Workwear - Workwear Sponsor for Plumbers Forums
Plumbase - PlumbersForums.net Sponsor
Power Shower Booster - Official PlumbersForums.net Sponsor
Test4Less PlumbersForums.net Sponsor

New Posts Threads Members

Top