Hi Guys,

I'm a complete novice trying to figure out a problem with my central heating/hot water.

Problem is that I'm getting HW when the programmer is set to CH ONLY. HW ONLY seems to be just fine (complete opposite of what most folk seem to have a problem with.)

I've got what looks to be a Y plan system with a Honeywell 4073 3-port valve with genuine Honeywell actuator fitted.

I've taken a look inside the actuator which seems to respond to all three possible positions as instructed by the programmer when powered up.

I've checked the valve spindle and it seems to be moving fairly freely (by hand). Although it has just a small range of movement, you can sense the rubber ball closing off the valves at each extreme of movement.

Can anyone think of a reason why hot water is still passing the valve and heading to the water heating tank?

Thank you!
 
Thanks for getting back to me Riley. Really appreciate that...

From the little bit of reading around I've done and from your suggestion, I reckon this must be a physical problem in the valve (a bad seal being made due to internal gunk or a worn rubber ball).

From what I can work out from the electrical operation and switching system, the actuator is making that final connection to the orange wire that finally activates the boiler in the CH ONLY mode. Like you've said, that valve must not be closing off properly, it's just that the actuator thinks that it has...

I'll leave this here for any other rookies like myself looking for the sequencing and electrical info: Y Plan central heating system
 
It's not uncommon for the balls to fail on these valves. There was a time that Honeywell supplied service kits but I'm not sure whether these are still available. Many pro's would just replace the whole thing; you can waste a lot of time fiddling with these things and success is not assured.
 

Reply to Honeywell 4073 issues in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I have a Vailant EcoTec Boiler with a Megaflo. These are controlled by a Honeywell controller. I have one 3 port diverter, where one of the outputs goes to a 2 port diverter prior to the Megaflo (I believe this is some safety feature). I have run into an intermittent problem where some...
Replies
5
Views
244
Hi All, Hope somebody can help :) I have a vented HW system with a pressurised Ch system but got bit of a annoying issue, when the hot water comes on all seems ok then after about 15/20 mins i started to hear a trickling noise from hw cylinder which i can also hear in the boiler. The central...
Replies
3
Views
471
Do people with this type of mixed flow temperature control have any problems with achieving the required manifold flow temperature? The one below I think is similar to the TIO Mixing unit. In the unit below, the hot (boiler) water enters from the bottom left, red arrow, up through the "mixing...
Replies
3
Views
564
I'm attending a wet underfloor heating system, it's an old one ..No flow meters, just adjustable valves on the returns with conventional actuators. Problem is , one loop (far right in photo) isn't heating the floor (timber suspended) . I've bled the loop via a hosepipe, shut off all the other...
Replies
3
Views
516
We have a Megaflo CL210 Cyclinder along with Evohome hot water kit and have come across a problem. We have had solar installed and a Myenergi Eddi solar diverter for hot water but when the Honeywell was originally installed they removed the bottom thermostat probe and inserted the Evohome...
Replies
8
Views
704
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock