I recently purchased a hive active heating. I currently have a Honeywell cm900 thermostat wired to my Worcester boiler. I'm just looking for advice as to how to wire the hive receiver which has the live, neutral, earth and 1,2,3,4. Please see pic of the Honeywell receiver. Just to add, there is an isolator switch at the side of the receiver.
IMG_20211002_090043.jpg
 
That’s unusual, I’m wondering if the second L is connected to A at some point? The 2 switching wires are Grey to Common (1 on Hive) and Black to NO (3 on Hive). L and N are straightforward and you can leave earth as is or park in Hive.

Do you have any test equipment?
 
That’s unusual, I’m wondering if the second L is connected to A at some point? The 2 switching wires are Grey to Common (1 on Hive) and Black to NO (3 on Hive). L and N are straightforward and you can leave earth as is or park in Hive.

Do you have any test equipment?
Thank you for your reply.
So I'm assuming that one L is coming from the boiler and the other from the isolator switch, both of these go in the L on the hive?
No I don't really have any testing equipment. Never needed but think I will do now owning my own house.
 
I’m guessing they’ve passed the boiler live neutral through as well from the isolator

So you should have a 3 core cable and a 5 core cable in there

So lives, neutrals and earth in the nest same as old

A -2 on the nest
B-3 on the nest
 
I’m guessing they’ve passed the boiler live neutral through as well from the isolator

So you should have a 3 core cable and a 5 core cable in there

So lives, neutrals and earth in the nest same as old

A -2 on the nest
B-3 on the nest
Yes three wire from the isolator and five coming from the boiler.
I noticed you mention nest but this is a hive, not sure if that makes a difference?
Number 2 on the hive is heating on, number 3 is heating off. So is nothing connected to common? I only ask as I was told to connect to 1and 3.
 
Yes three wire from the isolator and five coming from the boiler.
I noticed you mention nest but this is a hive, not sure if that makes a difference?
Number 2 on the hive is heating on, number 3 is heating off. So is nothing connected to common? I only ask as I was told to connect to 1and 3.

Sorry yes

A-1
B-3
 
Thanks for everyone's help. Hive is installed and working. Only thing I want to do now is extend the wire from the isolator and reduce the conduit to give more wire, all which I'll do when I buy cable. I just find the wiring a little tight due to the Honeywell having cable access via the sides but the hive is only from the bottom. Thanks again.
 

Reply to Hive wiring advice. in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

The fittings below are for a mixer bar attached to a self contained shower. i.e not a wall. The attaching screws have snapped. I could get two new brackets, dismantle that existing one and start again or I could try and re attach via those screws, removing the broken ones from the plate and wall...
Replies
1
Views
191
My son has an apprenticeship interview for to become a plumber and heating engineer. The have said there will be a multiple choice exam for this for suitability. The thing is my son panics during tests/exams. Is there any book I can buy him to practice the multiple choice test for the exam? What...
Replies
3
Views
405
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
229
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
239
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
316
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock