magicno1

Gas Engineer
Messages
252
Just been called out to a heatslave 20 25 old but in good knick.
Call was for the heating coming on when it is off on the prorammer.
Typically it wont do it while i was there!!!!
Any ideas????

Thanks
 
Depending on what type of diverter valve fitted. It maybe letting by.
 
My thoughts also. Could be a jammed microswitch in the diverter valve head.
 
Sounds like diverter valve cartridge or head faulty, take head off and see if cartridge pin moves up and down ok. Usually stick on dirty system. Easy to change.
 
Thanks guys
It doesn't do it all the time it's intermittent.
It's the grey Honeywell plastic valve.
 
Service the valve. Take off the head, remove the circlip and spring and unscrew the middle bit from the body (careful the circlip doesnt go flying off in the process). You will find a plastic plunger with O rings on it. CLean and grease this with heavy duty graphite grease. Put it all back together and away you go. You can buy service kits for these valves too with all the o rings and grease etc in them. I think theres a youtube video somewhere showing you how to do it.
 
Last edited:
Status
Not open for further replies.

Reply to Heatslave 20 25 in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
161
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
264
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
326
The fittings below are for a mixer bar attached to a self contained shower. i.e not a wall. The attaching screws have snapped. I could get two new brackets, dismantle that existing one and start again or I could try and re attach via those screws, removing the broken ones from the plate and wall...
Replies
1
Views
226
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
249
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock