hi i have a heatslave 12/14 boiler which the other day produced a small amount of black smoke on start up but worked fine today the boiler is running all of the time i have noticed that if i put my hand in front of the flue its as good as cold, luke warm and if i turn the water right down on the heat control the boiler stops as it should for that heat. i can also disconnect the solenoid on the oil pump and remove the photo cell which make no difference the boiler and oil pump keeps running as if ever thing was o.k. it does not lock out it was fitted with a new oil pump and motor bearings about 8 months ago, any help appreciated
 
Are you a homeowner? Are you saying if you disconnect the coil and cell the motor continues to run without lockout when when power is sent to the burner?
 
Are you a homeowner? Are you saying if you disconnect the coil and cell the motor continues to run without lockout when when power is sent to the burner?
yes motor continue to run i have also checked pressure at pump and i have pressure at the bleed screw but not at the pressure gauge port/screw and no pressure at the little pipe that connects pump to the nozzle .
 
To be honest it's hard to advise. Based on what you've said above my first check would be control box, although there could be more going on. You won't get oil flow to the nozzle if the coil is removed. This needs someone with the right tools to approach mythodically, I appreciate you want to fix this yourself, or are struggling to find an engineer but you're going to cause more problems than answers fiddling with it yourself. The very fact you've said you've played with the pressure adjusting screw means a pressure gauge and flue gas analyser are now needed to re-setup the burner for safe and reliable combustion even when the problem is found.
 

Reply to heatslave 12/14 in the USA area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
238
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
145
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
352
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
484
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock