One final question.

Should I fit the new 22mm auto bypass valve to replace what is there or should it go after the pump but before the motorised valves.

Thanks. Paul
 
Has a Plumber put that in?

Hi sorry couldn't reply properly earlier.

Yes following your previous advice a plumber did fit it, new pump, new valve and I fitted the magnaguard. It stopped for a few days but when the air was completely out of the system it started again. I questioned whether a 22mm auto bypass valve was required and he said this will do the same.
I am perfectly capable of fitting it myself but am not sure where to fit it. Do I install in the same place or before the valves but after the pump.

I even re installed the radiator and it bangs.
Cheers. Paul.
 
It will do there if it is 22mm and automatic. I am presuming you have a 3 mtr min loop from boiler and back to boiler via by-pass?

upload_2017-11-15_20-11-6.jpeg
 
It will do there if it is 22mm and automatic. I am presuming you have a 3 mtr min loop from boiler and back to boiler via by-pass?

View attachment 31830

The distance from the boiler to the by pass is about ten meters. I will change the size of the plumbing and use solder joints as it looks a bit messy. I can fit it somewhere else if it works better. I would rather it be correct. Wish I had done the work myself.

Does the pressure have to be regulated by the pump flow speed. Cheers.
 
The distance from the boiler to the by pass is about ten meters. I will change the size of the plumbing and use solder joints as it looks a bit messy. I can fit it somewhere else if it works better. I would rather it be correct. Wish I had done the work myself.

Does the pressure have to be regulated by the pump flow speed. Cheers.

It's fine there, 22mm with either a straight valve like the one I showed you or an angled one where the elbow is
 
I
Pump is on 2 as the system is quite large 12 rads.
Cheers.

If it works well it's fine. You want them on the lowest setting that works and gives the right flow and return temps.

With the valve:-
screw it shut, turn on the heating and hot water so both Motorised valves are open and the pipes start to get hot. Slowly open the Auto by-pass 1/4 turn at a time, (a few seconds in between turning), until you feel hot water flow through the by-pass. Then close it back around a half turn.


That's the best explanation I can give on a Forum. I would be going to greater lengths to set things up and balance the system if I were doing this in person but it will do!
 
I


If it works well it's fine. You want them on the lowest setting that works and gives the right flow and return temps.

With the valve:-
screw it shut, turn on the heating and hot water so both Motorised valves are open and the pipes start to get hot. Slowly open the Auto by-pass 1/4 turn at a time, (a few seconds in between turning), until you feel hot water flow through the by-pass. Then close it back around a half turn.


That's the best explanation I can give on a Forum. I would be going to greater lengths to set things up and balance the system if I were doing this in person but it will do!

Thanks I'll do it on Saturday and let you know how it goes.

Cheers.
 
Please do come back and tell us how you went on.
Hi.

I fitted the valve where suggested and unfortunately it still bangs, perhaps even louder. I can't get water to run through the valve unless I restrict the hot water flow, even with it turned down to 0.1 bar, the lowest it will go.

Picture attached.

Cheers.

IMG_3234.JPG
 
Okay. That's fine. If you were running it in flashing mode, then it would not be running fixed-speed, and the automatic bypass valve wouldn't be able to work as it should.
 
Okay. That's fine. If you were running it in flashing mode, then it would not be running fixed-speed, and the automatic bypass valve wouldn't be able to work as it should.

I'm not sure it is. I can only get water to flow through when I restrict the flow on the hot water.

I would have thought 0.01 bar would be open all the time. Any suggestions.

Cheers.
 
When you say restrict the flow on hot water,is this when the system is running eg demand from heating/hot water? The hot water coil should have a balancing valve on it that should be restricted (which from the pic you have one after the 2port) to stop the heat just whizzing around the coil and giving less to heating
 
When you say restrict the flow on hot water,is this when the system is running eg demand from heating/hot water? The hot water coil should have a balancing valve on it that should be restricted (which from the pic you have one after the 2port) to stop the heat just whizzing around the coil and giving less to heating

The balancing valve is fully open. When I mentioned restricting the flow I shut it off. Are you saying this valve should be half turned off or similar. Is this likely to contribute to the banging.

Cheers.
 
It should be restricted yes,but are you only getting flow through the by-pass valve when there is still demand for ch or hot water an your closing the balancing valve?
 
It should be restricted yes,but are you only getting flow through the by-pass valve when there is still demand for ch or hot water an your closing the balancing valve?

If I run the water and heating separately or even both of them together I can't get any water to pass through the bypass valve. I can only get it to pass through when I close the balancing valve with the hot water on demand.
 
Another point I forgot to add. If I turn the pump off at the fused spur, it doesn't bang. Don't know whether this has any bearing on the fault but thought I would mention it.

Cheers.
 
You don't really want water passing through the bypass when the valves are open so I wouldn't worry too much about that if the flow and return temps are ok at the Boiler.
I'm surprised it still bangs but you do need to rule things out like the lack of a by-pass before you can start to think of other possibilities,

I'll put my thinkin cap back on.
 
You don't really want water passing through the bypass when the valves are open so I wouldn't worry too much about that if the flow and return temps are ok at the Boiler.
I'm surprised it still bangs but you do need to rule things out like the lack of a by-pass before you can start to think of other possibilities,

I'll put my thinkin cap back on.

Cheers, it seems to be dragging on this but any suggestions I will try and I really appreciate all the help and advice.

Flow and return seem normal and all radiators get nice and hot.

I even tried balancing the system by restricting flow in the first radiator to warm up and so on.

I tried refitting the bypass valve with a normal 22mm isolation valve which I fully opened and it still banged. This would suggest an auto bypass is not required or not working even though the water is passing through and the pipes are hot.

When I am bleeding the system, when there is air present it doesn't bang. It's only when all the air is removed it starts to bangs.

Could the system just be full of glag as the filter is really dirty every week with bits of swarf/metal in it.

Thanks again.
 
Status
Not open for further replies.

Reply to Heating Bangs when switching off. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

P
  • Question
Boiler is SIRIUS THREE FS 70 Potterton commercial. Situation: We are small building contractors and my labourers managed to damage the radiator...
Replies
2
Views
147
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no...
Replies
6
Views
283
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
229
Hi, Later this year I am going away for a 2 week holiday and as the weather will be warm there is no need for the heating to be on and arguably...
Replies
1
Views
176
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
299
PSxxxxxx
P
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock