C

chelsea

Been to this boiler as it had a leak on the prv.

been back again as its still dropping pressure,prv is tight, no leaks in the house,i have checked everywhere and its baffled me as to where it can be, i checked the main exchanger, nice and dry.

i disconnected the filling loop to make sure it wasn't coming from there and that to is dry and left it for a few days and that's all clear.

Could it be the diverter or secondary plate exchanger from inside?

Any help or ideas on where to look would be a great help.
 
Last edited by a moderator:
Isolate the boiler overnight and then check the pressure when you turn the iso's back on in the morning, should point you in the right direction as to whether it's the boiler or system
 
As above
If it was the plate the system pressure would equalise with the mains (prv obviously at 3 bar would open if the main was above that )
 
OK the boiler has been turned off for a few days with the flow and return valves shut off, he came back today and pressure has dropped to zero, no water from the prv, is it pointing to expansion vessel?

i can't think of anywhere else it could go
 
Likely main heat ex kuffed and system water entering combustion chamber (through split in wall) then running out the condense
EDIT as said above :wheelchair:
 
Last edited:
Status
Not open for further replies.

Reply to Glow worm Betacom 24 in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
264
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
237
P
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
7
Views
218
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
292
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
160
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock