bradymd

Messages
11
Hi - I'm a homeowner, not a DIY person.
My 20 year old Gloworm boiler needs replacing.
British Gas quote is ok at £6100 for a 24kw replacement -valiant ecofit 625 system boiler. The tank/heat exchanger and copper pipework bring the price up.
OK so I object (rightly or wrongly) for the extra copper pipework ruining the look of the house outside so shop around. The gas safe rules demand it.
So a new company offer to charge £7000 to put a 12kw valiant pure system boiler (no additional pipework). But I don't feel I'm on top of their smooth explanation of how they can manage to do that. (Smart heating, condensing boiler etc). So, more expensive and less work really. This is not my world but Mr Google suggests this doesn't add up. The company seem OK .. website, livery, spiel, vans, google reviews. Not happy they didn't itemize and not happy they went £1000 over what I thought was already a high quote. Is there some magic they are offering? Or are they magicking away my money?
 

EvilDrPorkChop

Esteemed
Plumber
Gas Engineer
Messages
1,261
Depends what size of 4/5 bedroom house it is, in addition to how well insulated it is. What is the current size of your existing boiler? Most modern houses 4 bed new build houses will have a 12kw boiler for instance.

In terms of heating load, 12kw can be quite a lot of radiators. You could do it with HW priority thus you relieve some of the load.

I'd stay away from the EcoFit Pure too. Had a few issues with them. You want the EcoTec Plus system instead. Solid boiler.
 

ShaunCorbs

Staff member
S. Mod
Plumber
Gas Engineer
Messages
33,452
Solutions
3
Any of them done a Heatloss eg measured all of your rooms and windows ?
 

bradymd

Messages
11
Depends what size of 4/5 bedroom house it is, in addition to how well insulated it is. What is the current size of your existing boiler? Most modern houses 4 bed new build houses will have a 12kw boiler for instance.

In terms of heating load, 12kw can be quite a lot of radiators. You could do it with HW priority thus you relieve some of the load.

I'd stay away from the EcoFit Pure too. Had a few issues with them. You want the EcoTec Plus system instead. Solid boiler.
OK I didn't appreciate new builds for large houses would be 12kw. So thats interesting.
The House is a Town House (3 floors, built 2004) end of terrace. Can get cold on the ground floor.
The Glowworm Micron 70FF is 20kw I think.
There is 17 radiators and 3 bathrooms, so most sizing tables say more like 24kw.
I will read up now about EcoTec Plus.
 

bradymd

Messages
11
Any of them done a Heatloss eg measured all of your rooms and windows ?
Both british gas and the second plumber measured up to get the overall sq footage of the house. But "heatloss" I don't know about that really. There is some kind of heat loss on the ground floor but the house is not too bad otherwise for insulation - if thats what you mean.
 

EvilDrPorkChop

Esteemed
Plumber
Gas Engineer
Messages
1,261
OK I didn't appreciate new builds for large houses would be 12kw. So thats interesting.
The House is a Town House (3 floors, built 2004) end of terrace. Can get cold on the ground floor.
The Glowworm Micron 70FF is 20kw I think.
There is 17 radiators and 3 bathrooms, so most sizing tables say more like 24kw.
I will read up now about EcoTec Plus.
I suppose the question is why aren't they putting the same output back? As I assume the gas pipe is big enough for your current boiler.

As @ShaunCorbs They should do a heat loss calc if the output is in question. The online calculators are just generic.
 

ShaunCorbs

Staff member
S. Mod
Plumber
Gas Engineer
Messages
33,452
Solutions
3
The cold spots might be down to either too small of a rad in that room /sludged up one or an overall over-demand on the boiler

Tbh I would do a Heatloss Calc and see where you end up
 

bradymd

Messages
11
The cold spots might be down to either too small of a rad in that room /sludged up one or an overall over-demand on the boiler

Tbh I would do a Heatloss Calc and see where you end up
Using an online calculator the 13 rooms totals up to about 12 kw.
It's end of terrace town house and can be cold, doesn't catch the sun, there are 17 radiators.
So why would some sizing tables (and most plumbers including British Gas) says 24kw and other say 12kw? Madness...
 

Chuck

Esteemed
Messages
2,830
So why would some sizing tables (and most plumbers including British Gas) says 24kw and other say 12kw? Madness...
12kW seems low for the house you are describing unless it has had a lot of external insulation applied, which would be unusual and you haven't mentioned.
 

ShaunCorbs

Staff member
S. Mod
Plumber
Gas Engineer
Messages
33,452
Solutions
3
Using an online calculator the 13 rooms totals up to about 12 kw.
It's end of terrace town house and can be cold, doesn't catch the sun, there are 17 radiators.
So why would some sizing tables (and most plumbers including British Gas) says 24kw and other say 12kw? Madness...

Some just use rules of thump and oversize which doesn’t help did you work out if your rads are big enough?
 

Reply to Can a 12kw boiler ever heat a 4/5 bedroom house with 3 bathrooms? in the Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar threads

L
That helps a lot Nick, many thanks/to you and all again for the kind support!!
Replies
6
Views
471
lukeL81
L
Desktop987456
Thanks for your comments. The sensor was slightly off from the pipe which wasn't give accurate reading. Now sorted the sensor and gas usage on...
Replies
17
Views
909
Desktop987456
Desktop987456
S
Well the first thing i would be doing is Looking at a Viessmann system Boiler and a unvented cyclinder and have the bedrooms on one circuit and...
Replies
6
Views
1K
DAVE01
D
cailadd
Bathrooms with a shower are generally sized on 20 air changes and hour. That's the way we size them anyway. You'll get @ 15 air changes and hour...