My boiler is fine and I am getting heating downstairs and water on demand up and down. On the upper thermostat when i manually ask it to come on - the boiler is not getting the demand. The electric motorised valve is making a racket so I am thinking it might be to do with that. When the thermostat asks for heat the valve is nosiy and when it comes off noise disappeared. I established how to make sure the valve was open by hooking the switch to open but still nothing.

I have my guy coming out but he is so busy and I have heating and water I asked him to prioritise those with none. Anything I can do or check in the meantime? As said when I ask for heat downstairs all is ok
 
From the description it seems as though the demand signal from your zone valve is not being sent (or getting through). This could be faulty wiring, e.g. a loose connection, but is more likely to be an issue with the valve. There is a microswitch that is closed once the valve is fully opened by the motor. Depending on the condition of the valve, this may be fixed by replacing just the head or the whole valve.

Likely to be a fairly quick and straightforward job for your engineer.
 

Reply to Boiler OK - No upstairs Heating in the USA area at PlumbersForums.net

Similar plumbing topics

Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no issue, however, when running the heating the pressure drops. Im looking for some ideas on what could be causing this. I have no sign of pipe leaks...
Replies
6
Views
158
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
481
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
7
Views
192
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
345
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock